I have an 12V to 230V inverter in my car but get confused about ground it. The inverter is centre-tapped, means live-earth voltage is +115V, neutral-earth voltage is -115V, this gives an L-N voltage of 230V. Earth is connected to battery negative terminal, which I confirmed with multimeter. Live/neutral is not connected to anything on DC side. The inverter is powered by a secondary battery, which connects to starter battery via voltage sensitive relay. The negative posts of two batteries are always connected regardless of relay state, means the inverter Earth is connected to car chassis. However, this raises me some concern about safety:
Since both live and neutral have potential relative to car chassis, I will get electric shock if touching any wire. Would it be better to use an isolated DC-DC charger instead of connecting secondary directly to starter battery?
I have an RCD on the inverter output, which should theoretically trip if live/neutral touches appliance earth, or me touching live/neutral. But if I remove the connection between starter battery and secondary battery (make inverter a floating system), I will not get shocked when touching live/neutral, and RCD still works, right?
This problem confuses me for a long time because grounding the inverter doesn’t seem to provide any advantage. Instead, increases the risk of me getting electric shock.
Update:
I connected the inverter output to an RCD block, then connected a 10W LED flood light to L-E pins of the RCD block. The LED light turned on and RCD does NOT trip. I swapped the connection on LED flood light to N-E, and the light still illuminated, nothing happened to RCD. This proves that a centre-tap inverter will NOT trip an RCD if live/neutral is leaking to earth. Considering the inverter earth is connected to vehicle chassis, I cut the earth connection inside my inverter, makes it an IT system.
There is a guy on YouTube also tested RCD on an inverter, and the result is the same as mine. see link here
https://www.youtube.com/watch?v=GTqnkT_tO30
More expensive inverters may come with neutral-earth link. In this case, I believe it is safer to have an RCD on its output, then connect inverter earth to car chassis. IT system has its own disadvantages; in case of live touches car chassis, it still develops fault current through capacitive coupling. Having an RCD that quickly disconnect power source is better than letting it leak.
See Victron's book for more details about inverter earthing: https://www.victronenergy.com/upload/documents/Wiring-Unlimited-EN.pdf