0
\$\begingroup\$

As far as I've seen, low voltage distribution lines (3-Phase 440 volts) have four wires - three phases and one neutral (Ignore the earth cable). What should I do with the neutral line if I want to run an induction motor with a Delta-Star starter? I know that the delta connection does not need neutral. But in Star connection, should I connect the Neutral with the common terminal of the Star?

Online documents and books have ignored the neutral line. As far as I know, the output of the distribution transformer (11KV Delta / 440 Wye) sometimes gets unbalanced.

\$\endgroup\$

2 Answers 2

3
\$\begingroup\$

As far as I know, the output of the distribution transformer (11 kV Delta / 440 Wye) sometimes gets unbalanced.

That would be a very good reason not to connect the motor star / wye point to neutral. The motor - if all is well with the windings - will have its star / wye point centred between the three phases. Connecting this to neutral may result in uneven voltages applied to the motor's three windings.

\$\endgroup\$
3
\$\begingroup\$

N is not used from the source in a Squirrel Cage Motor (SCM) .

Rather a 3P2T transfer switch is used only from the 3Ph Delta source to boost the voltage per windings in Star Mode with <50% rated load torque for starting then switched to Delta across each pair for Run mode to reduce excitation currents and improve PF.

enter image description here ref

There are plenty of Youtube video explanations too.

\$\endgroup\$