You have three-phase power.
Total apparent power is 3 times \$S_{Phase}\$.
$$S = 3 \times S_{Phase} = 3 \times V_{Phase}I_{Phase} = 3 \times 277V \times 600A = 498.6 kV \cdot A$$
You have 277V / 480V, which makes it a wye connected source. Line voltages are \$\sqrt 3\$ times larger than phase voltages and line currents equal phase currents.
$$V_{Line} = \sqrt 3 V_{Phase}\ and\ I_{Line} = I_{Phase}$$
which means:
$$V_{Phase} = \frac {V_{Line}} {\sqrt 3}$$
Substitute into total apparent power.
\begin{align}
S &= 3 \times V_{Phase}I_{Phase} \\
S &= 3 \ \frac {V_{Line}} {\sqrt 3} I_{Line} \\
S &= \sqrt 3 \ V_{Line} I_{Line} = 3 \times 480V \times 600A = 498.8 kV \cdot A
\end{align}
You have to compensate for the differences between line and phase voltages and calculate total apparent power.