Let's start with this: -
If you had a DC voltage of 10 V and a 1 ohm resistor, the power dissipated in the resistor is 100 W because: -
$$P = \frac {V^2} R$$
The RMS value of 10 VDC is 10 VDC — it's the number you use to calculate power in DC circuits.
In simple sinusoidal AC circuits, if you have a peak value of 10 V, you will find that it dissipates in a 1 ohm resistor somewhat less that 100 W.
It will dissipate 50 W — and if you reverse the process to work out what peak sine voltage would cause it to dissipate 100 W you'll find it to be 14.14 V (approx).
Most engineers are so well-versed in doing this that it may seem, to the uninitiated, that there is no-theory behind it. I acquired this from the web: -
What you refer to as "Vm" I assume is an abbreviation for "Vmax" which I usually refer to as "Vpk".
Regarding 3-phase circuits, there is no fundamemtal difference except you are calculating power three times; one for each phase. If you have 3 resistors in a delta connection then, the power is the RMS Line voltage squared and divided by the delta resistor to which that line voltage is across. Repeat for the two other line voltages and sum all three.
That gives you 3-phase power.
If you have resistors in star-formation, you must use the phase RMS voltage (line divided by \$\sqrt 3\$) and calculate the 3 individual powers. Add them together to get power.
If the loads are imbalanced and there is no neutral connection, then there is more math, but I hope you get the picture.