I purchased a split core current transformer (SCT013 30A / 1V) and I want to make sure I don't need to install a burden resistor. The attached picture shows the guts of the transformer. Isn't the piece labeled '8ZRO' a burden resistor?
1 Answer
\$\begingroup\$
\$\endgroup\$
3
It is labelled 30A/V, so for that to be accurate it must have an internal burden resistor, to convert the current into a voltage (as indeed is shown in photo).
A current transformer without a burden resistor would be labelled something like 100A/5A. And this does then require an external resistor.
Be aware that with an unburdened CT the output wires must never be left open circuit under load (very high voltages will be developed).
-
\$\begingroup\$ You can see the difference called out in the penultimate line of the included spec sheet, where it says "voltage output built-in the sampling resistor" \$\endgroup\$– colintdCommented Feb 21, 2023 at 21:45
-
2\$\begingroup\$ I dont think high currents will develop - the whole point is that the current is proportional to the current in the wire - if the wire current is 30A, and the turns ratio is 1:1800, then the maximum current in the CT is 17mA, regardless of what the resistance is (even if its shorted). The potential danger is only the high voltage \$\endgroup\$– BeB00Commented Feb 22, 2023 at 2:32
-
\$\begingroup\$ You are if course right. The dangers of late night answers. Thanks, I'll correct. \$\endgroup\$– colintdCommented Feb 22, 2023 at 8:11
82R0
meaning 82 Ω (theR
serves as the decimal separator). \$\endgroup\$SCT013-030-30A-0-1V
then it will have an internal resistor. \$\endgroup\$