For some reason I can't wrap my head around how inverse time overcurrent relays work.

Here are some trip currents and times from this curve for the Schneider Electric, Square D, QO 15A miniature circuit breaker (click image for larger size):

Schneider Electric, Square D, QO 15A miniature circuit breaker, trip curve 910-1

100 ms: 90 to 150 A

1.0 s: 67 to 120 A

10 s: 27 to 45 A

22.5 A: 25 to 125 s

30 A: 9 to 40 s

45 A: 2.7 to 12 s

Here is what I understand so far. If 90 to 150 A of current flows through the circuit for 100 ms than the circuit breaker will trip. If it flows for less than 100 ms and returns to normal current then the circuit breaker won't trip.

But if 90 to 150 A of current flow for 50 ms and then 67 to 120 A flow for 0.95 s and then 30 A for 30 s and then returns to normal current. When will the circuit breaker trip and why?

I feel like I'm missing some crucial piece information and that's the reason why I can't answer this simple question but I have no clue what it is.

\$\endgroup\$
1
  • \$\begingroup\$ I think that the specific example that you make is too vague to be answered. As an example, 100 A for 1 s is compatible with your example, and the breaker would trip after 100 ms. 90 A for 50 ms and then 67 A for 0.95 s is also compatible, and theoretically the breaker would not trip. \$\endgroup\$ Jun 29 at 7:14

4 Answers 4

2
\$\begingroup\$

I feel like I'm missing some crucial piece information and that's the reason why I can't answer this simple question but I have no clue what it is.

The breaker has two parts.

  1. The magnetic part acts on instantaneous current - that is the surge rating of the breaker, say 10x the nominal current.

  2. The thermal part acts on the time integral of current. The integrator is leaky, and has some time constant. Due to the leakage, the running integral of the rated current is just below the threshold. In the short term, if the time integral of the current is above the threshold, the breaker trips.

    Thus, you'll notice that the I-t curve follows roughly the constant \$I\cdot t\$ product - since what trips the thermal part is the time integral. But, thanks to the leakage, as \$t \to \infty,\$ the curve transitions from \$I \cdot t\$ to \$I \to I_{rated}^-\$, where \$I^-\$ means "just below of".

\$\endgroup\$
4
  • \$\begingroup\$ So from what I understand about the tripping mechanism from what you just said is that its based on the fact that the time integral of the current is proportional to the change in temperature of the bimetallic strip which is proportional to its displacement. The breaker trips when the bimetallic strip displaces through a certain degree from its "normal" position and this is a constant value (given that it is initially at its "normal" position). \$\endgroup\$
    – xrosaber
    Mar 3 at 18:13
  • \$\begingroup\$ And this displacement is proportional to the change in temperature of the bimetallic strip which is proportional to the time integral of the current and hence why you are saying that the time integral of the current is roughly constant because the displacement of the bimetallic strip is roughly constant. \$\endgroup\$
    – xrosaber
    Mar 3 at 18:13
  • \$\begingroup\$ For example, in the scenario I gave above (assuming constant I*t), the running time integral of current is be equal to I*t for any given trip current and corresponding time. Taking 100ms and 120A as the constant, we get 12. Taking the running integral of the example I gave, 90\0.1 + 70*0.042=12. Therefore, the breaker would trip somewhere when 150ms (0.1+0.042) has passed. \$\endgroup\$
    – xrosaber
    Mar 3 at 18:13
  • \$\begingroup\$ Is there some degree of correctness in my interpretation of how the tripping mechanism works? \$\endgroup\$
    – xrosaber
    Mar 3 at 18:14
2
\$\begingroup\$

That is a thermal/magnetic breaker.

In the very large overload case(Here somewhere between 7 and 15 * rated current and up) the magnetic field trips the breaker with basically zero delay, and the springs then force the contacts apart clearing the fault within a single cycle.

For smaller overloads the thermal side takes over and has a delay, there is a bimetallic strip heated by the current passing thru it which if it gets too hot bends and activates the trip mechanism, in that sense it is RMS current responding (And yes the things behaviour varies with ambient temperature).

In normal operation you stay to the left of the breaker rating, with possibly the occasional foray into a multiple of the rating during startup surges and such, but still staying to the left of the grey area.

\$\endgroup\$
0
1
\$\begingroup\$

The circuit breaker is actually an integral of the transferred energy. The integral of i²t is what the circuit breaker graph is showing; if you know your current profile, you can calculate your cumulative energy and compare it with the circuit breaker energy graph.

\$\endgroup\$
0
\$\begingroup\$

The power in the bimetal strip is actually proportional to the square of the current. At a point where the heat loss is not very significant, the approximate trip time is inversely proportional to the current squared. For 10 sec., it takes about about 2.25 x rated current. For 1 sec., it takes a about 2.25√10 x rated current (actually bit less (~6.9x), because at that current, the heat loss is even less significant). At 7-15 x rated current (that big vertical area), it can trip from either the bimetal strip or the magnet. The magnet is only just pulling hard enough to trip it and can take up to about 1/4 sec. Above 15x, it trips as fast as the magnet can trip the mechanism (1 cycle max.).