1
\$\begingroup\$

I'm replacing a pump: 400 V, 4 kW, 2 pole. It is a wye-delta startup.

The control circuit is working correctly, as I've double checked it and extended the lead to feed another 4 kW motor. When it starts up in wye, I'm reading 9 A but then 57 A when it switches to delta. I've tested the windings insulation (1000 MOmh). Each winding read 0.95 ohms.

The pump is a Grundfos Model: PN-SN A-96501772-10001084 Type: CRN15-4 A-FGJ-A-E-HQQE Motor is tagged: MG112MC2-28FT130-H3.

I've tried increasing the run time in Wye from 2 up to 15 secondes to make sure the pump gets up to speed.

Any thoughts?

\$\endgroup\$
6
  • \$\begingroup\$ One wind is shortened. 1000MOhms is insulation. Measure the winds resistance. \$\endgroup\$
    – user263983
    Commented Jul 10, 2023 at 16:25
  • \$\begingroup\$ Need to know the controller and motor numbers and specs \$\endgroup\$
    – Voltage Spike
    Commented Jul 10, 2023 at 18:56
  • \$\begingroup\$ I'm reading 0.95 ohm on each winding \$\endgroup\$ Commented Jul 11, 2023 at 8:00
  • \$\begingroup\$ The pump is a Grundfos Model: PN-SN A-96501772-10001084 Type: CRN15-4 A-FGJ-A-E-HQQE Motor is tagged: MG112MC2-28FT130-H3 \$\endgroup\$ Commented Jul 11, 2023 at 8:04
  • 2
    \$\begingroup\$ Is the wye-delta switch correctly wired? If a phase was reversed in one configuration, I suspect you could plug-reverse at the moment of switching \$\endgroup\$
    – user16324
    Commented Jul 11, 2023 at 15:14

2 Answers 2

1
\$\begingroup\$

If you can disconnect the motor shaft from the load, suggest starting it DOL (delta connected) and measuring currents in each phase. All phase currents should be the same, if not, then as others have suggested there may have a fault in one of the windings, which won't always show up when running the motor in star (Y). You can also connect it in Y, run it, and measure the voltage at the centre node (the star-point) and see if this is close to 0V (should be less than, say, 10% of line voltage). If not, then at least one winding is not right. Of course, you should never connect the star point to neutral. Cheers.

\$\endgroup\$
4
  • \$\begingroup\$ I have between 6.2 and 6.5 amps on each phase. Is this significant enough to show an issue on the winding? As for the centre node to ground, i am reading 5 volts. Thanks for your help \$\endgroup\$ Commented Jul 13, 2023 at 10:20
  • \$\begingroup\$ Follow-up questions: Re: currents you measured: Was that with the motor in Y or delta? Was the motor shaft disconnected from the load and the shaft turning normally? If yes, then it is unlikely that the differences in currents you measured (6.2 to 6.5A) indicate a problem. Re: voltage of star-point: what is to neutral to earth voltage? This has to be measured while the motor is drawing current at conductors located as close to the motor as possible. When you first had the problem, what was tripping out, the motor thermal overload, or the circuit breaker? \$\endgroup\$ Commented Jul 15, 2023 at 4:08
  • \$\begingroup\$ Question 2: How long was the motor running in delta before the trip occurred? Does the motor run indefinitely (say, about 30 seconds) and get up to full speed while in star without tripping out? \$\endgroup\$ Commented Jul 15, 2023 at 4:09
  • \$\begingroup\$ Open-transition star-delta starters are notorious for causing circuit breakers (not thermal overloads) to trip - this has been known for decades, this article from the 70s is useful reference: mastercontrols.com/Articles/Wooddall/TA_RWood.htm That paper suggests that a solution may be to swap two pairs of cables to keep motor direction the same, but which changes the magnetization of the windings. I recall seeing an app note on this, but cannot seem to locate it now. \$\endgroup\$ Commented Jul 15, 2023 at 4:19
0
\$\begingroup\$

Is the time delay for change-over, from wye to delta, adequate?

The change-over is to be effected only after the motor has attained its rated speed in the wye configuration.

Please check, for correctness, the power wiring also.

enter image description here

Image credit: Siemens

\$\endgroup\$
2
  • \$\begingroup\$ It was set to 2 seconds. I uped it to 15 seconds to see if that would help, but the result is the same. Thanks \$\endgroup\$ Commented Jul 13, 2023 at 10:21
  • \$\begingroup\$ Okay. Have you checked the power wiring? \$\endgroup\$
    – vu2nan
    Commented Jul 13, 2023 at 14:02