I´m currently designing power transformers in a pretty basic way, using AWG tables for the section of the copper wire, and not knowing what are the real losses, just overdesigning.
Three phase transformers: Secondary power between 3-15 kW, star-delta or delta-delta configurations. Input voltage: 380 Vac. These start to give me troubles when the power is more than 5 kW approximate.
Single phase transformers: Secondary power between 100-3000 W. Input voltage: 220 Vac. These start to give me troubles between 1800-3000 W.
Specially three phase ones, I've searched a lot of these ones, and not being able to understand the calculations. In my case, they are working in saturation 100% of the time
Let's say that 200 A 24 Vdc are required at output. If the design is delta-delta, it will be:
V = 24 Vdc / sqrt(3) = 13.85 Vac
It = 200 A
I ( tower ) = 200A / sqrt(3) = 116 A
P = 1600 W per tower
(added information⬇⬇⬇⬇)
Core selected:
Maximum power of core: (5.1 cm x 9 cm) x (5.1 cm x 9 cm) = 2106 W
I primary = 1600 W / 380 V = 4.2 A
Turns x Volt = 45 / core area = 45 / 45.9 = 0.98 Turns x volt
Primary side turns: 380 V * 0.98 = 372 Turns
Secondary side turns: 13.85 V x 0.98 = 14 Turns
(added information⭡⭡⭡⭡)
Then, I would search the section of wire in an AWG table.
Are the calculations ok? I'm missing losses somewhere? Why when I make the bigger ones, it can't reach the calculated current?
Thank you!
(example of calculations for a single phase transformer)
The problems are …
please don't comment comments asking for clarification or complementary information: edit your post.then directly to the battery
gives an awful conversion_ratio/Crest factor. \$\endgroup\$