In and of themselves, sure. Note that, as current-limited devices, "switching" could also include a short circuit (in which case the generated photocurrent is looped back through the PV array itself, raising its temperature modestly). An open circuit is generally preferred for various reasons.
There may be extenuating reasons to taper or delay the turn-off of some megawatts. Depending on distribution line length and resistance, availability of power in the general area, what rules the regional utility has for connecting large loads or sources, there may be undesired over/under-shoot of voltage at turn-off, or the transient response of the grid is otherwise impacted (may cause phase and frequency shifts as well as change in voltage, affecting other customers, generators, etc.).
1MW I think is on the low side of where this might be a concern, but, more just to say, at some point, for a load/source large enough, some coordination is needed, between the main generators on the grid, and the load in question. Large industrial clients, generating stations, cross-region links (im/ex-porting power), etc. are examples where such communication is beneficial. So, perhaps 1MW arrays, no, but a whole farm of them, totaling some 100s MW, likely.