4
\$\begingroup\$

Actually, we have 1x30HP, 2x10HP motors working at our workplace. When we start the motors there is a lot of torque generated due to which our grid supply charges us penalty every month.

We need information about the device(s) that are used to control the torque.

While doing some research, I got to know that I can get myself set up control panel that has capacitors either separately on each motor or on my 100kVA transformer. This will control the torque as well as give me saving on electricity bill.

Kindly help in this regards.

\$\endgroup\$
6
  • \$\begingroup\$ You should post the motors control schematic in order to get adequate help. \$\endgroup\$
    – johnfound
    Oct 22, 2013 at 10:39
  • \$\begingroup\$ You're probably best off buying an off the shelf motor controller (often sold as frequency converter). Trying to do this passively will take lots of time and won't nearly be as good or safe. They're only a couple hundred bucks on ebay, much cheaper than investing a couple engineering hours. \$\endgroup\$
    – user36129
    Oct 22, 2013 at 10:50
  • \$\begingroup\$ how often each day do the motors start? Do you get billed on number of starts. If not, what criteria does your bill consider to charge you the excess amounts? \$\endgroup\$
    – Andy aka
    Oct 22, 2013 at 10:51
  • \$\begingroup\$ Active power filters are another solution.. I have no idea the price tho.. \$\endgroup\$
    – Spoon
    Oct 22, 2013 at 11:24
  • 2
    \$\begingroup\$ You are confused. Your utility does not penalise you for excessive torque. They may penalise you for excessive peak demand (startup current) or for violating half-hourly average power factor limits. \$\endgroup\$ Oct 23, 2013 at 14:36

4 Answers 4

6
\$\begingroup\$

Note that your question states that you want to reduce the starting torque, but you actually want to reduce the starting current.

There are a few ways to reduce the starting current of a three-phase induction motor. In rough order of cost:

  1. Reduced Voltage starters

    These methods apply a reduced voltage (say 50%) to the motor on first starting. This reduces the current draw to 50%. After the motor attains enough speed, the voltage is increased from 50% to 100%.

    Note that the torque is reduced as the square of the voltage, so with 50% voltage the motor will only develop 25% torque. You need to ensure that this torque is enough to turn the motor's load from a standing start.

    • Series resistance starter - put resistors in series with the motor's line terminals to limit the amount of current drawn on starting. The resistors are shorted out after the motor has reached approximately half speed.
    • Star-delta starter - the motor is started with its three-phase terminals connected in wye. If you have a 415VAC three phase supply, that means that only 230VAC is applied to each winding and the current is similarly reduced. Once the motor is up to speed, switch from star connection to delta connection, which applies the full 415VAC.
    • Autotransformer starter - uses an autotransformer with two voltage taps to apply a low voltage on motor starting (with corresponding low current), switching to full voltage after the motor has gained some speed.
  2. Soft starter - an electronic device that starts the motor at a low voltage, with corresponding low current, and continuously increases the voltage until full speed is reached. The difference between this and rotor resistance, star-delta, and autotransformer starting is that the voltage is increased steadily, as opposed to in one sudden step. This is more gentle to the motor and load.

  3. Variable speed drive (also known as VSD, VFD, VVVF) - an electronic device that starts the motor using full rated voltage, but at a lower frequency. The most expensive of all methods, but also the best, as it can apply very high torque from a standing start.

    As the name suggests, VSD's also allow variable speed control, which no other motor starting method does.

It doesn't sound like you have a wound-rotor induction motor, so I will neglect to mention rotor resistance starting.

More on this topic can be found by searching for "three-phase induction motor starting". You should be able to find application notes and guides written by equipment manufacturers, that will go into more detail about how the above methods work and what equipment you can use to implement them.

\$\endgroup\$
0
\$\begingroup\$

there are a few way to limit the starting current of an induction machine (at the expense of acceleration). The simplest is some series resistance that is shorted out You can add some capacitors in parallel to compensate for the lagging current.

\$\endgroup\$
0
\$\begingroup\$

You either need a soft start, or vfd.

http://en.wikipedia.org/wiki/Motor_soft_starter

http://www.automationdirect.com/adc/Shopping/Catalog/Drives

\$\endgroup\$
-1
\$\begingroup\$

I have researched about this in the local market and got to know that people have installed a device called Power Factor(A panel board which has capacitors). Good quality capacitors are from Hyundai or LG i heard.

Many people have installed them with their transformers rather than on individual motor. For e.g you have 100 kva transformer, but people have installed Power Factors which can handle load of 200kva to carter any torque from motors etc. The power factor actually handles all the load of the workplace and includes all motors working.

Kindly guide if this is the correct solution, If yes than which company has good quality and economical ones.

\$\endgroup\$
9
  • 1
    \$\begingroup\$ Power factor correction will not reduce your motor's starting current. (It won't reduce your starting torque, either, though that has nothing to do with your problem.) \$\endgroup\$ Oct 23, 2013 at 14:37
  • \$\begingroup\$ While this is mistaken, it's based on zeeshan's research attempt to solve their own problem, so it doesn't need to be penalized. \$\endgroup\$ Oct 23, 2013 at 14:47
  • 1
    \$\begingroup\$ If your intent with this post is to provide additional details and then seek clarifications, please edit this content into the original question. While answering one's own question is encouraged on this site, that only applies when you have a definitive solution to the problem stated, and are sharing it to benefit future visitors with a similar problem. \$\endgroup\$ Oct 24, 2013 at 10:27
  • \$\begingroup\$ @ChrisStratton votes are to mark if an answer is technically valid or not. \$\endgroup\$
    – Kortuk
    Oct 24, 2013 at 13:41
  • 1
    \$\begingroup\$ @ChrisStratton the point of votes is to automatically sort by technical quality, if the answer is wrong then it is likely the worst form of "not useful". Should we all upvote for trying and tell the user their answer is correct? \$\endgroup\$
    – Kortuk
    Oct 24, 2013 at 15:21