A contactor, like a relay, is an electrically controlled switch. Contactors generally have higher voltage and current ratings than relays, but the ratings overlap with no specific dividing line. Contactors are intended to control the power supplied to motors, electrical heaters, groups of lights and other loads that require an undefined level of "high power." The word "contactor" is essentially defined by its use in product literature.

Filter by
Sorted by
Tagged with
0 votes
1 answer
284 views

Switching 400V motor with 5V

I'am trying to make an automatic irrigation system using an Arduino, a moisture meter and a water pump. The issue is that I can't figure out whether there is some relay/contactor type component that ...
LordBertson's user avatar
0 votes
2 answers
525 views

Contactor: when and how to use it

I hope my question is not too stupid. I'm controlling a brushed 48V 50A motor with a motor controller and I use two gel batteries as a power supply. I would like to use a low power signal to switch ...
Marcus Barnet's user avatar
0 votes
0 answers
44 views

What is the max current of this contactor? CDC65-24

I'm attempting to power a 50kW DC Fast Charger with 3 phase 277/480V. It needs ~55kW which is 66A per phase. I'm trying to find a contactor. This one is CDC65-24. It is a 3 pole, 100A continuous. ...
Lost Puppy's user avatar
0 votes
1 answer
314 views

Two Switches to Control a Pump

I have a water tank that I want to fill up with a well. I have a float switch at the top of the tank and another float switch in the middle of the tank. What I want to do is have the pump only turn on ...
Michael's user avatar
1 vote
1 answer
2k views

Vacuum Contactor Wiring Diagrams

In reviewing the following wiring schematics for a vacuum contactor, I can't wrap my head around why things are the way they are. Source > Downloads > Catalogues Wiring Diagram #1, Size 4 Contactor ...
C. Lange's user avatar
  • 1,437
0 votes
1 answer
331 views

How to connect voltage protection relay to contactor?

Could you help me connect a voltage protection relay (VPR) to a contactor? I'm not sure how to connect the relay output terminals (NO, NC, COM, etc.) to contactor control terminals A1 and A2 in the ...
Pavin Joseph's user avatar
0 votes
2 answers
129 views

Digital control of contactors

We are trying to control a bunch of 3 phase contactors using an HMI. The contactors' coils are activated by two lines of the 240V 3 phase source (L1 and L2). We are trying to figure out if the ...
Ivan Leon's user avatar
0 votes
1 answer
54 views

Can a contactor be used as a temporal logic bit as in PLC?

I want to design a control logic circuit using relay logic. I want to have a bit as a marker as in PLC. Can I use a contactor for this function and then use auxiliary coils as a latch as in PLCs.
suyol854's user avatar
  • 310
0 votes
1 answer
338 views

Which suppresor device will be use for 2pole AC contactor 240v coil voltage in coil as well as contact side?

I need an AC contactor for a 1 hp motor. For the contactor safety I'm goint to use the suppression device on the both coil and contact side. Please suggest me which suppressor device will be use! I ...
SENTHURA MOOERTHY's user avatar
1 vote
1 answer
464 views

How Does Line Frequency Affect Coils of a Contactor?

I am using a generator as my source voltage, which produces 240VAC @ 240Hz. I was planning to use the following contactor from TE: CONTACTOR 4PST 40A 240V In the datasheet it says this contactor's ...
Mark Wright's user avatar
7 votes
3 answers
9k views

What lubricant is suitable for switch contact?

I have this expensive DPDT switch (20A 250V 2hp) which the only problem is dirty encumbered inside. The encumbrance is made of carbonized material and some kind of wax and dirty electrical contacts. ...
Fred Cailloux's user avatar
0 votes
1 answer
362 views

Auxiliary contacts on contactor to power solenoid valve

I'm just trying to introduce cold water in to industrial shredder. Connected cold water supply to machine. That's not good because when I forget to turn off water it will overflow. I have not seen ...
bbarclays's user avatar
1 vote
0 answers
189 views

Why are contactor coils connected to two different safety relay outputs?

When looking through a manual for a safety relay, I began to wonder why the coils of the load contactors (K3 and K4 on pages 14-15) are always connected to two different NO contacts of the safety ...
relatively_random's user avatar
1 vote
4 answers
7k views

Are three-phase contactors rated per pole or in total?

Are three-phase contactors rated per pole or in total? For example, have a look at this datasheet for a random three-phase contactor: datasheet In the datasheet it says that for AC-3 loads (1) the ...
Marko Gulin's user avatar
  • 1,511
0 votes
0 answers
300 views

Switching a power contactor from an arduino / raspberry

I'd like to switch a power contactor (such as this one : https://www.legrand.fr/pro/catalogue/31925-bipolaires-250-v/contacteur-de-puissance-cx3-bobine-230v-sans-commande-manuelle-2p-250v-25a-contact-...
Golgot's user avatar
  • 127
1 vote
1 answer
169 views

CC12 Contactor is Confusing

I am attempting to use this relay, the CC12, to turn the 120VAC power to a motor/motor controller on and off using a 24VDC signal (These voltages are specified in the datasheet.), and I've gotten ...
Blapor's user avatar
  • 13
1 vote
1 answer
985 views

IGBT contactor design

I found this circuit in an older post. I was thinking about using this in place of a contactor to break under load. The load would be at 500V 300A DC. There would be overcurrent protection in line ...
EEDAVEE's user avatar
  • 11
0 votes
0 answers
520 views

Controlling 2-pole contactor using Arduino

I am working with Packard C230C contactor to develop own EVSE. For a simple start i just want to toggle contactor using Arduino. OpenEVSE is already doing it. Just want to know how do they do it and ...
Suraj Jorwekar's user avatar
1 vote
2 answers
566 views

Contactor/relay rating for bypass function of soft start circuit

I am designing a soft start circuit for a 70KVA, 70A, 480/230 delta/star transformer, since the fuses kept blowing without. I've been using 3 NTC thermistors rated for 80A in series with the lines ...
Ezraneut's user avatar
0 votes
2 answers
1k views

Automatic cut mains power on a thunderstorm

I am a software engineer with only a basic experience with electric/electronic engineering. I live in a rural area subject to thunderstorms, my house is the end of the line from street poles. It's ...
TNT's user avatar
  • 101
0 votes
2 answers
430 views

Industrial contactor frequency influence

I'm thinking of using industrial motor contactors at the output of a 3-phase electrical generator. An example here : CONTACTOR DATASHEET The only difference / problem is that the electrical ...
VoltsAndNuts's user avatar
3 votes
2 answers
4k views

About Contactor Lifespan

Newbie here regarding contactors and relays, i had this contactor datasheet https://www.gavazzionline.com/pdf/CC50-CC65.pdf. I'm trying to identify how long the contactor would last and I find the ...
Mheruian's user avatar
  • 311
0 votes
2 answers
8k views

Contactor's Coil Current

YuCo YC-CN402-24V CN-PBC402-24V DEFINITE PURPOSE CONTACTOR with a Packard PF42440 Control Transformer Class II Foot Mount 40VA 24V to activate the 2vac coil. The circuit is a 220v 20amp motor. My ...
Sprinkfitter's user avatar
0 votes
1 answer
43k views

Problem in star delta starter in air compressor

I am a beginner in electrical engineering. I am trying to understand how motors are connected in a star and delta system. I studied the star delta starter from this link. It describes the connection ...
user_fs10's user avatar
  • 851
3 votes
1 answer
323 views

Which relay will last the longest?

I'd like to control a 20 amp, 240 volt AC resistive load with a heavy duty contactor. The contactor I have is a Siemens 3TX7130-0DB03 rated for 30 amps, and DPDT. I was originally going to switch ...
Billy left SE for Codidact's user avatar
1 vote
1 answer
5k views

Starting (inrush) current of a resistor (heater)

We are going to purchase a 48kW electric drying oven. As we know the AC motors have big starting current and a special starting equipment is needed - Star-delta, soft-starter, inverter and etc. What ...
Teodor Bochev's user avatar
0 votes
1 answer
1k views

Can I operate a 120VAC contactor with a DC power supply

If yes, What would be the voltage and amperage for DC to operate the 120 VAC contactor? And, Can I connect two contactors in parallel, and actuate both using DC ? I need it for a project, where I can'...
Neil Dsouza's user avatar
16 votes
6 answers
11k views

Contactor vs Relay

As known, contactor is used to switch higher capacity than relay. But there some relays can switch high current too, such as, some power relays can switch current beyond 100A, and there are contactors ...
diverger's user avatar
  • 5,738
1 vote
1 answer
851 views

Interface submersible water pump with microcontroller using contactor relay

I am making a automatic water level controller for my home. I am using a MCU to turn ON/OFF submersible water pumps using a float switch to detect water level in overhead tank. This pump has a start ...
Archana Wadhwani's user avatar
1 vote
0 answers
455 views

Trailing edge dimmer to activate relay/contactor

I would like to take the 240V feed from a trailing edge dimmer that is driving LED lamps and use it also to activate a contactor or relay. This would in turn run a 230V fan. (Reason: want to have a ...
Bagpuss's user avatar
  • 11
0 votes
1 answer
114 views

Using regulator capacitor bank for a motor

I want to use a regulator capacitor bank in a small facility that has a machine so based on the power factor it insert the capacitors. Each 30 seconds the motor power factor is 0.4 and for 10 seconds ...
Mohammad Yousefi's user avatar
0 votes
2 answers
1k views

switching device for motor

This query is from my project on automatic motor switching of water tank. My question is that what should be the rating of switching device(relay or contactor) for single phase induction motor (2hp 8A ...
Rohith K's user avatar
0 votes
2 answers
645 views

Suggestions on how to control a 1000W DC motor

I would like to find out the best solution to safely control two 1000W DC brushed motors by using a atmega328p. In particular, the DC motors are rated: 1000W, 50A, 24V, 2400 RPM. I have a radio ...
Marcus Barnet's user avatar
0 votes
1 answer
841 views

Main contactor of star delta motor starter

Why do some control circuits of star delta starter use two normally open auxiliary contacts of the main contactor and others use one? To me only one normally open should be enough. Can a contactor ...
Carson's user avatar
  • 1
0 votes
1 answer
144 views

can contactor, water level sensor and heater all live in parallel on the same circuit

I want to connect my 3000w (220v) water heating element to a 220v water level sensor Automático de Nível so that the heating element won't turn on when there is no water present. But the level sensor ...
Charles Spencer's user avatar
1 vote
2 answers
5k views

Automatic transfer switch VS Using a Reversing Contactor with Circuit Protection

We have a an industrial control system that utilizes a 480VAC 3 phase 10 Amp service. For redundancy reasons, we wanted to add an automatic transfer switch to the system to switch between two ...
Greg's user avatar
  • 11
0 votes
1 answer
618 views

Mechanical Contactor for High Voltage DC - Substitute with Semiconductor

To switch 1kV DC at 5A, I usually use a mechanical contactor (<- Wikipedia) that switches both highside and lowside of a resistive load. Any suggestions on a semiconductor (or non-mechanical part) ...
m00wn's user avatar
  • 342
3 votes
3 answers
690 views

Contactor control circuit overvoltage

I have a 12VAC-controlled contactor (ESB 20-20, rated for 12V @50Hz), and a 220/12 transformer that I intend to connect to the contactor. Unfortunately, rather than 12V, the transformer outputs 14V (...
Maxim's user avatar
  • 31
0 votes
1 answer
728 views

Correct design for large contactor circuit?

After some advice here I'm wondering if this is the correct design of my circuit. I'm now using a SSR as the control device to the contactor. The diode, I believe, should not only protect the SSR ...
C.J. C's user avatar
  • 43
2 votes
1 answer
263 views

Relay/Contactor for 30A inrush, 250mA steady

I'm struggling to find any relay or contactor even close to the specs I need, and I've contacted many manufacturers. This is controlling a large contactor, so draws a 30A 24DC inrush current. It then ...
C.J. C's user avatar
  • 43
2 votes
2 answers
2k views

Using capacitors to supply peak current

I hope this thread is allowed. Based upon my previous topic, which turned out to be the exact opposite of what I needed to accomplish, I have a few questions. I have a 240W 24V Supply: https://www.us....
C.J. C's user avatar
  • 43
0 votes
3 answers
3k views

Suppressing contactor coil inrush, is this possible?

http://www.kvc.com.my/EnterpriseChannel/SharedResources/Datasheet/0/?ProductId=1000066755&Filename=SCHNEIDER-LX4-FH024.pdf I am trying to operate a 24VDC coil with an inrush of approximately 30A, ...
C.J. C's user avatar
  • 43
0 votes
1 answer
272 views

What is "x Us" in a contactor coil specification?

I have a data sheet that gives the coil pickup voltage as "0.85…1.1 x Us] and coil dropout voltage as "0.3…0.6 x Us". I am assuming that Us refers to the nominal or specified coil voltage, but why is ...
frog_jr's user avatar
  • 101
0 votes
2 answers
1k views

How to detect a plug is connected to a socket

I have a plug and socket. Before I turn on the power supply from a contactor, I need to detect if the plug is connected to the socket via a microcontroller. Any ideas on how to do this? The plug I am ...
bhuvan's user avatar
  • 63
4 votes
1 answer
6k views

Using a Contactor or Relay to switch between two DC power sources?

I want to power a motor with a battery, however the complication arises as I want to have two power sources and be able to switch between them. The context of this problem is for an electric vehicle. ...
Joe's user avatar
  • 55