This is probably a stupid question but I am new to IO link sensors.

When using IO link technology with a PLC (siemens s7-1200) can you connect devices that are not IO link sensors?

For example say I wanted to connect an existing normal push button to a IO link master, is it possible to cut the plug of the IO link cable and connect the button with the 3 required cores( positive, negative and the signal wire)?

\$\endgroup\$

3 Answers 3

2
\$\begingroup\$

When using IO link technology with a PLC (siemens s7-1200) can you connect devices that are not IO link sensors?

For example say I wanted to connect an existing normal push button to a IO link master

It depends on the IO Link master. Some allow you to turn off the IO Link functionality on a per port basis and use them as a standard input.

It's usually a waste of a master port though as you can get devices that convert 8 or 16 binary I/O points into IO-Link. Examples include:

https://www.ifm.com/us/en/category/055/055_020

https://www.balluff.com/local/us/productfinder/#/ca/A0009/cg/G0903?cal_iolink

\$\endgroup\$
1
\$\begingroup\$

An IO-Link system consists of an IO-Link master and one or more IO-Link devices

That's a quote from Wikipedia IO-Link and basically it means that master and slaves have to be compatible: -

An IO-Link system consists of an IO-Link master and one or more IO-Link devices, i.e. Sensors or Actuators. The IO-Link master provides the interface to the higher-level controller (PLC) and controls the communication with the connected IO-Link devices.

When using IO link technology with a PLC (siemens s7-1200) can you connect devices that are not IO link sensors?

No, you can't.

For example say I wanted to connect an existing normal push button to a IO link master, is it possible to cut the plug of the IO link cable and connect the button with the 3 required cores( positive, negative and the signal wire)?

No, you can't.

\$\endgroup\$
1
  • 1
    \$\begingroup\$ @David777 why have you unaccepted the answer? \$\endgroup\$
    – Andy aka
    Commented Dec 7, 2020 at 15:31
1
\$\begingroup\$

say I wanted to connect an existing normal push button to a IO link master, is it possible to cut the plug of the IO link cable and connect the button with the 3 required cores

No. You would need to get an IO-link digital interface device and connect your push button to the interface. The interface would then communicate with the PLC over an IO-Link cable.

An IO-Link system is a form of point-to-point computer network connection. It runs a specific computer network protocol over the IO-Link cable between an IO-Link master and an IO-Link device, which could be a sensor (input) or actuator (output). The master and the devices need to have some built-in computing ability in order to implement the IO-Link protocol.

If you have an intelligent sensor (i.e. one with a built-in microcontroller) it can implement the IO-Link protocol itself and be plugged in directly to an IO-Link cable. Here's a random example of a pressure sensor with an IO-Link interface.

However a normal push button doesn't have a microcontroller, it can't implement the IO-Link protocol itself and therefore it can't be plugged in directly to an IO-Link cable. Instead you need to use an IO-Link sensor device as an intermediate device between your pushbutton and the IO-Link cable. You'll need an IO-Link sensor with a digital input. (In this context "digital" means a single line carrying ON or OFF information.) You'll need to wire your pushbutton to a digital input on a sensor. The sensor will read the state of the pushbutton and send the state over the IO-Link cable to the IO-Link master and then on to the PLC. (IO-Link digital input connectors also seem to provide 24VDC and ground connections so you can power your pushbutton circuit.)

While I suspect the idea of standardising IO-Link is that any manufacturers' products can be used, as you do have a Siemens PLC Siemens also make an IO-Link digital sensor, the K20. (If you click on the booklet icon to the left of the 3RK5010-0BA10-0AA0 model number a browsable list of other IO-Link devices should appear, if not already visible.)

This may seem a roundabout way of getting pushbutton input into a PLC but you specifically asked about IO-Link. An alternative is that your PLC may have digital inputs to which a pushbutton could be wired directly.

Siemens themselves or your usual PLC supplier should be able to provide you with technical help on how to use these products. A search engine should find a selection of documents and videos to let you learn more about IO-Link.

\$\endgroup\$
2
  • \$\begingroup\$ How does this digital interface device differ from a IO link master device? Have you got any links of products? I don't quite understand what you mean \$\endgroup\$
    – David777
    Commented Dec 7, 2020 at 10:26
  • \$\begingroup\$ @David777 In IO-Link jargon a device is a peripheral that connects to an IO-Link master over an IO-Link cable. I've extended my answer. Please comment if anything still isn't clear. \$\endgroup\$
    – Graham Nye
    Commented Dec 7, 2020 at 18:43

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge you have read our privacy policy.

Not the answer you're looking for? Browse other questions tagged or ask your own question.