I have to measure a current of 500 A (50 Hz) using a 500 A/5 A CT with a uC. In my circuit, I have a 2.5 V reference/offset and the voltage will be measured about this offset value. There are low cost 5 A/5 mA PCB mount CTs available. Is possible to short the output (5 A) of 500 A/5 A, through the 5 A/5 mA, then use a burden resistor of 1k on the 5 mA and thus measure the 500 A current?
Is possible to short the output(5A) of 500A/5A, through the 5A/5mA , then use a burden resistor of 1k on the 5mA and thus measure the 500A current ?
Yes, you can do this but you are compounding errors. I suspect that the main CT (500/5) will have a fairly decent specification regarding errors/tolerance. But, the 5 A/5 mA might significantly degrade the overall accuracy.
I understand the problem; to get a 2.5 volt peak with 5 amp peak output requires a resistor of 0.5 Ω and, if the AC is a sinewave, the RMS will be 3.536 amps. This will lead to a power dissipation in the 0.5 Ω burden of 6.25 watts.
So, my preference would be to use a significantly smaller burden such as 0.1 Ω and live with the 1.25 watts of dissipation. Of course, the peak voltage will now only be 0.5 volts but, a half-decent op-amp can restore this towards 5 volts p-p.
In my circuit, I have a 2.5V reference/offset and the voltage will be measured about this offset value.
You say you want to use a 1 kΩ burden resistor with a current of 5 mA. If that current is RMS then, into a 1 kΩ resistor, the signal voltage would be between +7.071 volts and -7.071 volts superimposed on the 2.5 volt reference i.e. well beyond your MCU input range.
  • \$\begingroup\$ I was planning to use one of those generic PCB mount 5 A/5m A CTs. Will this error be linear , so that I can trim it in software ? In case I use the opamp, I am assuming i will need a dual supply (+/-) for the OpAmp ? Thanks much ! \$\endgroup\$ Commented Aug 24, 2022 at 5:18
  • \$\begingroup\$ Yes I goofed up on the 1k resistor calculation, of course. \$\endgroup\$ Commented Aug 24, 2022 at 5:20
  • \$\begingroup\$ If you pick the correct op-amp it should work from a power rail of +5 volts and 0 volts but, bear in mind that you should aim for the maximum current to be slightly within that range (maybe 50 mV either side. The error of using a 2nd current transformer may not be very linear due to various things but, if you want, link me the data sheet for the 5 A/50 mA device. \$\endgroup\$
    Commented Aug 24, 2022 at 6:03
  • \$\begingroup\$ Just a tad confused, The output from the CT will have a negative swing, so a rail to rail 5V OpAmp will not be able to handle it ? \$\endgroup\$ Commented Aug 25, 2022 at 5:51
  • \$\begingroup\$ Not able to get a datasheet , but this one : electronicscomp.com/5a-single-phase-ac-current-sensor-module \$\endgroup\$ Commented Aug 25, 2022 at 5:52