5
According to the datasheet of this power supply, the output voltage goes from 0~60 VDC. If the output can't be negative, why does it have a negative rail beside ground? Why not just have ground?
In a circuit, should I connect my circuit's ground to the negative or to ground of this voltage?
  • 7
    \$\begingroup\$ I have seen degreed engineers confused by this. \$\endgroup\$
    – Mattman944
    Commented Jun 4 at 13:49
  • \$\begingroup\$ Does this answer your question? Shall I connect '-' terminal of power supply to earth GND (green terminal)? \$\endgroup\$
    – Justme
    Commented Jun 4 at 23:33
  • \$\begingroup\$ Is this supply isolated? \$\endgroup\$
    – Voltage Spike
    Commented Jun 5 at 0:29
    \$\begingroup\$ This sort of confusion is one big reason why electricians refer to the "-" line as "common" or "neutral", to explicitly differentiate it from an earth/safety ground. Engineers still confusingly call it "ground", mostly due to tradition. \$\endgroup\$
    – bta
    Commented Jun 6 at 15:04
  • \$\begingroup\$ Does calling it potential difference instead of voltage help? \$\endgroup\$ Commented Jun 6 at 15:20
5 Answers 5
15
The power supply itself has two output terminals, labelled \$\boldsymbol{+}\$ and \$\boldsymbol{-}\$, and produces up to 60 V between them. Remember that voltage is defined only as a difference between two points; neither of these has a defined voltage relative to earth.
It also has, for convenience, an earth terminal on the front, labelled . Neither of its outputs are connected to earth—almost all bench power supplies have a floating output—so if you need an earth-referenced output, you can tie either the positive or negative output to earth ground. It can also be a convenient place to plug in an antistatic wristband, or anything else you may need grounded. This terminal should, in a properly designed power supply, be connected via a low-impedance path to the ground prong on the mains plug powering the PSU.
The circuit being powered should always be connected between positive and negative; it's just that sometimes it's desirable to tie negative to earth. Or to tie positive to earth, in some cases (like telecommunications equipment), or even to have some other point entirely referenced to earth.
  • \$\begingroup\$ If my circuit has any other connection to earth ground, I don't connect the power supply earth ground. A scope, PC, or other test equipment is usually grounded to earth. \$\endgroup\$
    – Mattman944
    Commented Jun 4 at 13:52
  • 4
    \$\begingroup\$ @Mattman944 Sometimes a single-point ground is desirable, yes. It's not always, though; sometimes (contrary to occasional over-broad advice--ground loops are not always as big a deal as people think and sometimes you really need good shielding) you want as much grounding as possible. It's not always trivial to determine the best grounding strategy. \$\endgroup\$
    – Hearth
    Commented Jun 4 at 14:12
  • \$\begingroup\$ @Hearth Ground loop can be a problem. If you connect the green and negative terminal together at the lab supply, and you power a board with a few amps and that board is also connected to say with USB cable to your earthed desktop PC, if the return wire between board and lab supply ever disconnects by accident, you have all those amps returning from board via USB cable and mains earth wiring back to the supply. Which means you most often use a floating supply for safety, unless the floating board has no other earth connections, then it may be earthed to reduce picked up mains hum. \$\endgroup\$
    – Justme
    Commented Jun 4 at 23:49
    \$\begingroup\$ @Justme Right. I'm not saying ground loops are never a problem, but rather that they are not always a problem, or sometimes less of a problem than you would have without them. I've seen people take measures to prevent ground loops where it really wasn't an issue, and the measures they took just made problems in the system due to poor grounding. \$\endgroup\$
    – Hearth
    Commented Jun 5 at 3:29
  • \$\begingroup\$ I've seen someone melt a probe by not realizing their very expensive scope did not have isolated probes, unlike the previous model they had used. A ground loop was created through the ground clip of the probe, the scope, the protective earth line, the benchtop power supply, and the DC power connector. The object under test was trying very hard to create a 24 V potential between the probe clip and the power supply negative. Fortunately the scope survived. \$\endgroup\$
    – AI0867
    Commented Jun 5 at 13:15
8
If the output can't be negative,...
Whether a voltage is positive or negative depends on how it is measured. The negative (black) terminal is the reference against which the positive (red) terminal is measured. placing meter probes such that the red probe is on the black terminal and the black probe is on the red terminal will measure the voltage as negative. So the output voltage can be negative.
The word ground needs clarification. The green terminal is connected to the chassis and power earth. It is not a negative "rail". It is used to connect a circuit under test to a common mode voltage (not necessarily 0V) that is also common to the operator. It is commonly called zero volts, but be careful. It is zero volts only if used that way. Zero volts is arbitrary depending on where the black probe of the voltmeter is placed.
This is a laboratory voltage supply. Having a separate power earth connection provides flexibility for circuit testing, with or without power earth a attached. It allows a static dissipative connection (if implemented properly) to power earth to an otherwise insulated circuit.
Test equipment (oscilloscopes for example) probes can have a power earth connection already, so a floating circuit may be convenient.
Here ground is being used to mean circuit common in one sense, and the negative of the power source in another sense. This is often used to represent zero volts in a circuit. The negative (black) terminal of a voltage source is not ground unless it is connected to ground. Be careful not to confuse negative with ground.
The phrase "ground of this voltage" is ambiguous. The red terminal is positive relative to the black terminal. It does not "have a ground" in any meaningful sense.
Either the positive or negative terminal may be connected to power earth. There is no general requirement that the negative terminal should be grounded.
The red and black terminals should be considered like a variable battery connected between them, "floating in the air. When a conducting path is closed from the red to the black electrons will flow out of the black terminal and into the red terminal. The green terminal is not involved.
The green socket is in fact chassis earth and connects to the protective earth (PE) that comes into the power supply from the wall socket. That green socket is usually galvanically isolated from the red and blue socket circuit.
You may not want to tie your negative terminal to chassis ground when there is the possibility of picking up white noise off that ground. Floating the circuit and tying it to a different ground is sometimes better.
When using multiple supplies, you might want to tie all negative terminals to a "single point ground" and then tie that point to chassis ground.
As explained, the positive, negative, and Ground are electrically isolated. You can bond or reference either polarity to Ground. The ground terminal is the equipment chassis and AC Equipment ground feeding the power supply. In a DC system, you can float the output or make it a grounded system.
One primary reason you would use a grounded system is to provide simple, cost-effective over-current protection devices (OCPD) like fuses and breakers. Just like an AC grounded system, you bond one of the polarities to the Ground with a large enough conductor to safely handle any fault current likely imposed on the system. You install an OCPD on the ungrounded circuit conductor to protect all circuit conductors. The disadvantage of a Grounded System is they are dangerous and prone to unnecessary outages.
If you float the system, you must provide OCPD, which means you install an OCPD on each polarity or phase. An alarm or monitoring circuit is required to detect a Ground Fault and alert maintenance personnel to schedule an orderly shutdown to make repairs.