Ok I have the following circuit and data (when the subscript is "ef" it means "rms" values):
I am asked to determine the paramenters of the transformer r1 L11, L22 and LM with the given experimental data.
I had no problem extracting data from the open circuit experiment. Using the fact that the active power is given by $$P=r_1 I_{rms}^2$$
I found $$r_1=10 \Omega$$
Then applying induction law in both primary and secondary leaves us with:
$$u_1(t)=r_1i_1(t)+L_{11}\frac{di_1(t)}{dt}$$ $$u_2(t)=-L_{M}\frac{di_1(t)}{dt}$$
Applying phasor notation and taking the rms values will lead us to obtain
$$L_M=\frac{U_{2_{rms}}}{\omega I_{1_{rms}} }=31.83 mH$$ $$L_{11}=\sqrt{(\frac{U_{1_{rms}}^2}{I_{1_{rms}}^2} - r_1^2) \frac{1}{\omega^2}}=55.13 mH$$
Ok and there is no more data we can extract form the open-circuit experiment.
Passing to the short-circuit experiment I will obtain from induction law again:
$$0=-L_{M}\frac{di_1(t)}{dt}-L_{22}\frac{di_2(t)}{dt}$$
Which leads to
$$L_{22}=\frac{L_M I_{1_{rms}}}{I_{2_{rms}} }$$
Problem now is I don't know the value of the root-mean square of current 2 and have no idea how to find it out. My guess is that I need to use the reactive power. But how? I know from Poynting complex theorem:
$$P_Q= 2\omega ((W_e)_{av} - (W_m)_{av})$$
But, and that is another question I have and would like to get ans answer on? How should I apply this formula. For the electrical energy, should I take the capacitor? But what's the voltage value? The same as the open-circuit experiment? And for the magnetic energy? What inductances should I consider? Do I need to calculate an equivalent circuit?
I'm really confused and would appreciate some help. Thanks!
  • \$\begingroup\$ You seem to be calculating the mutual inductance by considering the open circuit secondary but I can't see how this can be done without knowing both the coupling, the output voltage and the secondary inductance. Maybe I missed something? Also, the primary inductance (L11) does not involve U2 although I get the same answer - maybe you typoed. \$\endgroup\$
    Nov 28, 2018 at 18:34
  • \$\begingroup\$ Hi! It can be done applying the induction law as I did! Because I obtain it with the relation between u2 and i1. Because the current i2 is zero... Yes it was a typo, thanks! How would you calculate the coupling and the secondary inductanc? \$\endgroup\$ Nov 28, 2018 at 19:42
  • \$\begingroup\$ On the short-circuit test, the primary voltage is lowered so there's the rated secondary current drawn at secondary short circuit. \$\endgroup\$
    – Janka
    Nov 28, 2018 at 19:48
  • \$\begingroup\$ Janka I don't understand what you said and how it helps me \$\endgroup\$ Nov 28, 2018 at 19:51
  • \$\begingroup\$ Anyone please?? \$\endgroup\$ Nov 28, 2018 at 20:43
The closed circuit experiment will yield two equations instead of one:
$$\begin{align} u_1(t) &= r_1i_1(t) + L_{11}\frac{di_1}{dt} - L_M\frac{di_2}{dt}\\ u_2(t) &= r_2i_2(t) - L_M\frac{di_1}{dt} + L_{22}\frac{di_2}{dt} \end{align}$$
(Note that the signs may need to be changed)
Meaning it will have 2 equations and 2 unknowns (\$i_1(t)\$ and \$i_2(t)\$), which can be solved.
[Edit]
For your short-circuit experiment and when using phasors, this would result into something like:
$$\begin{align} \underline{U_1} &= \left(r_1 + j\omega L_{11}\right) \underline{I_1} - j\omega L_M \underline{I_2}\\ 0 &= -j\omega L_M \underline{I_1} + \left(r_2 + j\omega L_{22}\right) \underline{I_2} \end{align}$$
The solution to this set of equations will be two complex values for \$\underline{I_1}\$ and \$\underline{I_2}\$. You can take the absolute value like with any phasor.
$$\underline{U_1} = U_{RMS}\cdot \sqrt{2}$$
$$I_{RMS} = \sqrt{\frac{\text{re}[\underline{I}]^2+\text{im}[\underline{I}]^2}{2}}$$
And you can calculate the complex power as well
$$\underline{P} = \underline{U_1}\cdot\underline{I_1}^*$$
  • \$\begingroup\$ How the hell do I work with this equations? I need to pass to phasor form but then how do I take the module? Because I will have the sum of phasor I1 and phasor I2 I have no idea on how to take absolute values. Can you be more specific than that? \$\endgroup\$ Nov 28, 2018 at 21:25
  • \$\begingroup\$ Can you help me please? \$\endgroup\$ Nov 29, 2018 at 0:25
  • \$\begingroup\$ can you help me please? \$\endgroup\$ Nov 29, 2018 at 18:04