I am trying to connect an AC line filter (rated for 115/250VAC) on the load side of a 24VAC transformer (part# BPD2G, datasheet here).
The first filter model I used is Delta's 03DBAW5.
03DBAW AC Line Filter
From the datasheet, I couldn't really figure out what each wire was. I assumed the green/yellow cable is the neutral line, so I connected that to the ESD cable on my workbench to ground it. I also figured, since this is supposed to be chassis mounted, that the metal shield of the filter should also be grounded, so I clipped one of the side mounting holes to the ESD ground cable as well.
I then connected the input brown and blue wires to the output screws of the 24VAC transformer, which was plugged into a 120VAC wall socket. The output brown and blue wires of the filter I connected to the power input of my device (which can take up to 60VAC/DC and has a full-bridge rectifier plus step-down converter and LDOs to power the device at 5VDC and 3.3VDC).
I measured the voltage at the output of the filter (input to my device) and saw 12VAC across it. Before I could measure the voltage at the input to the filter (it should read 24VAC from the transformer), I noticed that the outlet/transformer had started smoking and immediately unplugged it.
What have I done wrong? Is this filter only usable on the high side?
  • \$\begingroup\$ It sounds like your load is shorted. Does it work when connected to the transformer without the filter? \$\endgroup\$
    – Dave Tweed
    Jun 21, 2019 at 1:02
  • \$\begingroup\$ Did you know that all transformers for a given VA size must be derated by at least 35% when driving a bridge capacitor load? and current is limited by large Cap or battery ESR !! \$\endgroup\$ Jun 21, 2019 at 1:21
  • \$\begingroup\$ @DaveTweed Too late. I must have shorted/overloaded the device during this testing (proven by hooking it up to a power supply after this catastrophe) and will now have to rework it before hooking it up again. Could very well have been shorted, but it's a device I've powered several times from a PS recently with no issues until now... \$\endgroup\$
    – YNGVV
    Jun 21, 2019 at 17:31
    \$\begingroup\$ warning: "green/yellow cable is the neutral line". NO, it is normally the earth (protective ground), which you connected correctly to ground. But don't call it "neutral", which is very different thing. \$\endgroup\$ Dec 23, 2021 at 9:36
The wire colours on that filter match the standard European scheme of:-
Brown = live/hot/phase
Blue = neutral
Green/yellow = earth/ground
There are many different arrangements of Line filters designed for grid input to target device. The above is only a few. Others used cascaded CM chokes with a midpoint filter.
I see a few problems in your setup.
  1. Do not connect green to Neutral. Grn/Yel is always Earth ground.
  2. Do not connect Neutral to your ESD cable on your workbench.
  3. The filter will not do its job if you connect the Grn/Yel Earth Ground wire to Neutral.
  4. Do not use a line filter designed for high voltage lower current to the output of your transformer which is lower voltage, high current. PUT IT ON THE 120Vac ( or 240Vac) side. But low voltage low current is OK.
My hunch is your 24Vac load was excessive due to the buck converter and caused some resonance with the line filter on your wallwart.
I can only make an experienced guess, because I do not have your measurements or schematics.
  1. Re-wire the filter with a 3 pin plug and socket and add heatshrink to insulate exposed solder joints.
  2. Follow my advice in points 1~5
  3. If you ever notice such voltage loss in future, warning current is excessive and you should use an appropriately rated inline input fuse or PTC ( in an enclosure as it gets hot when activated.)
Conclusion
The Full-Bridge cap DC to Buck DC-DC regulator caused thermal issues for your brick, possibly exacerbated by the line filter. The line filter installation info on the web was never searched.
Post Mortem
After looking at the spec link for transformer rated at 20VA 24V , again this must be derated when used with an diode bridge cap load to no more than 15VA. Then the DC–DC converter should soft start and run NO MORE than the same, I conclude you have the wrong transformer VA rating for the job or a bad startup load.
All transformers are rated @ Vout at max VA and expected to drop 10% Vac at this load from no load . When you drop 50% as in your measured voltage, that should have been your clue it was going to smoke. The fine wire primary cannot dissipate the heat fast enough so it is chosen to drop no more than 10% including secondary losses. Thus drawing possibly 5x the rated load dropping another 50% implies your load was the cause of the smoke. You must verify your design start surge current with sense R’s or ammeter to ensure it has a soft start by adding ICL’s to limit the starting current enable a holding current. These are inexpensive from Digikey.
  • \$\begingroup\$ 1-2. I did connect the grn/yel to Earth ground via the ESD cable. What's wrong with that? 3. This seems to contradict point #1. I didn't connect it to neutral, I connected it to ground. 4. Fair enough. I suspected as much, but my device does not draw more than an amp of current. Wrt your conclusion, I did do plenty of line filter installation research but none of it was as specific as the instructions you are giving now. Why would the buck cause thermal issues or excessive loading? \$\endgroup\$
    – YNGVV
    Jun 21, 2019 at 17:28
  • \$\begingroup\$ I misunderstood "I assumed the green/yellow cable is the neutral line," It is actually for earth ground direct connection. Is bench direct earth ground? 3. connecting earth connection to Neutral would not bypass EMI noise to earth. Connect to primary side only. Some chances for LC anti-resonant frequencies with higher impedance secondary source and we have no idea what your SMPS does with that.. \$\endgroup\$ Jun 21, 2019 at 17:34
yellow/green = Earth
Blue = Neutral
Brown = L1
The rest is self explaing in the datasheets schematic, snip shooted below.