1
\$\begingroup\$

I build a quite lot of projects to learn electrical engineering, and since I was first introduced to what's called a fuse around 2 years ago and I always put one in my high voltage 220V mains for protection, but when I worked with precious LiPo batteries, I wanted to add a fuse for protection.

The problem is that what's written in my pack of fuses is "220V 250mA" here comes the question, what make a the fuse fuse or pop-open circuit? Is it the current rating or the voltage rating?

As I am a student who loves experiments, I went and did an experiment, where I used a 7.4V 1AH LiPo battery which was rated at 20C and hooked a 1 ohm load, theoriticaly I should be able to draw 7.4 A but due to resistance of wiring I was able to draw around 4 A (used high watt resistor). When I hooked up the fuse (220V 250mA) in series with the load, I was expecting it to pop open, but it took around 1~2 seconds till it popped up, although the rating was at 250mA 0.25A which is way less than the 4 A drawn by my dummy load.

I wanted to know if is this normal for an electric fuse, or my fuse is very bad manufactured? As a side note my fuse works perfectly fine in 220V circuits

I done a bit of research if there is anything called low voltage fuse, found some webpages,but I couldn't understand anything

One of the pages I saw is: here

My fuse type is the normal glass fuse. enter image description here

this is not my image, source : here

In short what pops a fuse (sorry but is pop the right word to use in such thing?) Is it the over specified voltage or over specified current or it's the power through it? And in the other side what kind of fuses used in low voltage application like fuses in digital multimeter? Is it the same fuse I have?

Thanks in advance.

\$\endgroup\$

4 Answers 4

4
\$\begingroup\$

Fuses blow due to heat, and heat is due to current via \$I^2R\$. Therefore, what blows a fuse is the current.

However, a fuse needs to blow with a large enough gap that the voltage behind current cannot overcome the gap. A fuse with a 1mm gap isn't going to be able to interrupt a current with 10,000V behind it (it might make a massive, long-lived arc that eventually extinguishes at best, and at worst the 10,000V will cause sparks across the gap or melt and weld the gap.) That's what determines the voltage rating of the fuse. The voltage rating is irrelevant while the fuse is not blown.

High voltage fuses do have different features such as sand or other materials that melts or buries the contacts when the fuse blows to reduce arcing or explosions.

As you found, fuse blow times are inexact and vary. If you look at the datasheets of some fast-blow and slow-blow fuses, you will find charts of how long it takes for the fuse to blow at a rated current. At 100% of the rated current, the fuse could take a very long time to blow (could run for minutes on end). At 200% or 500% of the rated current, it blows much faster. Don't expect a fuse to behave ideally and instantly blow within 1ms as soon as you exceed the rated current.

I cannot explain why it took 1-2 seconds to blow at 1600% overload though.

\$\endgroup\$
3
  • \$\begingroup\$ Most likely, the current was a lot less than predicted, as a result of the resistance of the fuse. that would mean that the fuse takes a lot longer to blow. \$\endgroup\$
    – Simon B
    Commented Feb 8, 2020 at 21:42
  • \$\begingroup\$ @SimonB Yeah. OP never did say how he knew 4A was the load current; whether it was measured or calculated. \$\endgroup\$
    – DKNguyen
    Commented Feb 8, 2020 at 21:44
  • \$\begingroup\$ Thanks so much for your answer, much appreciated, and as I see you're asking about how I knew the current drawn, I used a digital multimeter to measure it , and it was around 4.6 or 4.3 Amps, I just approximate it to 4Amps for making numbers easy. \$\endgroup\$ Commented Feb 8, 2020 at 21:58
3
\$\begingroup\$

In addItion to DKNguyen nice, elaborated answer:

Because 220V is typically AC and I doubt you bought an expensive DC fuse:

Never use a AC fuse for a DC application.

A fuse melts, leaving a gap between its internal wires. By definition, AC current makes zero current crossings at 50 or 60 Hz. This zero crossing will make any arc will distinguish. However, the next period a new arc may appear because the breakdown voltage is exceeded again.
Due to melting, the distance between the internal wires increases and so, the breakdown voltage increases. Eventually, no new arc can originate because the breakdown voltage is not overcome anymore and the recreation of a new arc will cease eventually.
AC fuses 'rely' on that feature.

It is quite possible the fuse in your application arced for a small longer time due to the LiPo battery providing DC current.
Once an arc is established, its length is only limited by the available energy, not by voltage.
The melting of the internal wires will also continue, increasing the length of the arc. The arc will eventually cease due to the application failing to provide enough energy to sustain the arc.

\$\endgroup\$
2
  • \$\begingroup\$ Thanks so much but no, I haven't bought a DC fuse yet, it's not sold in my local shops... But what I understand from you that you recommend using a DC fuse rather than an AC fuse right ? \$\endgroup\$ Commented Feb 8, 2020 at 21:43
  • 1
    \$\begingroup\$ Yes, I recommend using a component where it is meant to be used for. But, as you witnessed, the AC fuse may eventually work as well, albeit not at the expected/calculated moment. However, it may as well trigger not at all. So, if you keep an eye on your application and are able to interact appropriately (disconnecting the power source e.g.) and you know what you're doing, you may decide to still use an AC fuse. But when developing a product for commercial market for 'clueless' people, it is absolutely a no go. \$\endgroup\$
    – Huisman
    Commented Feb 8, 2020 at 22:15
2
\$\begingroup\$

A fuse is just a very low-valued resistor with the intention of self-destructing under specified circumstances. The "low-valued" aspect is application-dependent. It's possible to have a fuse with \$10\:\Omega\$ that would be good in one application and terrible in another.

A conventional fuse like yours will experience ohmic heating. If this becomes sufficient to cause melting, the link material may have been selected so that it constricts (pulls apart) and one or more arcs form (fast blow.) This greatly increases the circuit resistance and its Ohmic heating and, in rapid progression, it consistently "fails open" and the circuit is interrupted. (As it is intended to be.)

Not all fuses are alike in the way they self-destruct. Materials are carefully selected. Those materials that rapidly constrict will be fast-blow. Other materials are more like a conventional wire and heat up gradually and eventually fail. These are slow-blow. Hopefully, all of them are well-designed for their application.

The design involves not only the selection of an appropriate conducting amalgam for the fusing wire, but other additions to modify the overall behavior (a larger, added dissipation surface over part of the fuse, for example.) It also requires extensive testing against manufacturing variability (no two are exactly alike, but all of them must behave within prescribed parameters.)

As a fuse begins to fail open, as the material changes state from a solid towards either a liquid or gas, energy that once was increasing the sensible heat will instead go into latent heat during that transformation. This is transition between the pre-arc and post-arc time periods. The Meyer integral is often used to compute the pre-arc phase.

Physicists would prefer action, as the fusing point is really measured in Joule-seconds (and Planck gave that the name action a long time ago.) There is both a melting integral and an arcing integral for a fuse. These, when summed, are called the clearing integral of the fuse. You won't usually see all those details from manufacturers, though.

The basic idea of a fuse is that you need to deliver a certain number of Joules and do so within a certain amount of time (or less) in order to guarantee the fuse opens. This is also called the all-fire specification. So, for example, you may have a fuse that gives an all-fire specification of \$500\:\text{mJ}\$ in \$50\:\text{ms}\$. You need to know details of the fuse to know if you can achieve this, of course. But note that the all-fire specification avoids details such as current, resistance, etc., as it's really about material science and the fuse structure and physical design and expected operating environment.

Most manufacturers will instead only specify the melting integral. This is often found under a table column labeled \$I^2\,t\$. The manufacturer units are wrong, but it does specify the important details. The complication is that the resistance of the fuse evolves as it opens up and specifying the units that physicists like wouldn't really be of much help to engineers. And since the action is proportional to \$I^2\,t\$, that's sufficient for all engineering purposes. Keep in mind that \$I^2\, t\$ is usually only valid under adiabatic conditions, without external heat transfer beyond what the manufacturer can normally predict. If you do something extra that provides added routes for dissipation, the fuse will behave differently.

\$\endgroup\$
1
\$\begingroup\$

The problem is that what's written in my pack of fuses is "220V 250mA" here comes the question, what make a the fuse fuse or pop-open circuit? Is it the current rating or the voltage rating?

Primarily, it's the current that blows a fuse. The fuse has no way to know what the voltage of your circuit is. The 220V rating stamped into the fuse is the maximum voltage it can safely break. If you use it in a circuit above the rated voltage, then instead of breaking the current, it may just arc across the terminals.

When subjected to a large overload, you can use the manufacturer's I²t rating to estimate how quickly it will blow. So if a 250mA fuse has an I²t of 0.25 and you put 10A through it, it should blow in time t=0.25/100 seconds.

At lower currents, you would need to look at the curves in the manufacturer's data sheet to see how quickly they are likely to blow.

As I am a student who loves experiments, I went and did an experiment, where I used a 7.4V 1AH LiPo battery which was rated at 20C and hooked a 1 ohm load, theoriticaly I should be able to draw 7.4 A but due to resistance of wiring I was able to draw around 4 A (used high watt resistor). When I hooked up the fuse (220V 250mA) in series with the load, I was expecting it to pop open, but it took around 1~2 seconds till it popped up, although the rating was at 250mA 0.25A which is way less than the 4 A drawn by my dummy load.

The time it takes for a fuse to blow varies considerably, by design. Ones stamped "T" are slower, and ones stamped "F" are faster. Slow-blow fuses are intended for protecting circuits where a large current surge is expected on start-up.

You also need to allow for the resistance of the fuse itself. The fuse you used may have had a resistance of around 0.6 ohms, which means the current you were putting through it was less than what you expected.

\$\endgroup\$
2
  • \$\begingroup\$ "The fuse you used may have had a resistance of around 0.6 ohms, which means the current you were putting through it was less than what you expected." Yeah you're right didn't put that in mind. My measurements were on the load only, before adding the fuse. \$\endgroup\$ Commented Feb 8, 2020 at 22:01
  • \$\begingroup\$ You (I think correctly) state \$I^2t\$ determines when a fuse blows. Shouldn't Primarily, it's the current that blows a fuse. correspond with that? So, shouldnt time be added? \$\endgroup\$
    – Huisman
    Commented Feb 8, 2020 at 22:12