What kind of power and voltage can the cable in the photo possibly drive and why is it composed of a lot of small cables? What if the diameter of the single copper cables were a little bigger? How should one pick the right diameter for the given voltage/wattage combo?
link to the original post
  • \$\begingroup\$ here are no notion of scale in your picture. We have no idea if that cable section is small or huge. Please add a scale to the picture or at least give us the figures. \$\endgroup\$
    – Blup1980
    Commented May 22, 2014 at 17:18
  • \$\begingroup\$ @Blup1980 that's why I added the link to the original post, anyway, here it is another picture with some reference to it imgur.com/bBnezbN \$\endgroup\$ Commented May 22, 2014 at 17:19
5
What kind of power and voltage can the cable in the photo possibly drive?
That is a high voltage cable. Guessing from the thickness of the XLPE insulation (white material) it is for at least 132kV or higher.
Edit: According to the Reddit OP, the cable has 1,750mm² copper conductor. This is a huge cable. (Anything above 630mm² is unusual; anything above about 1,200mm² is a special order which the cable company would not usually make.) Such a cable would be capable of carrying roughly 1,600 amps. Assuming the voltage is 132kV three-phase that is 365 MVA or about 292 megawatts at 0.80 power factor.
Here is a similar cable I had at work for (I think) 300kV. It would be capable of carrying at least 100 amps (probably much more), or about 100 MW - enough to power an entire city CBD all on its own.
Why is it composed of a lot of small cables? What if the diameter of the single copper cables were a little bigger?
The conductor is multi-stranded so that it can be bent for installation. A solid copper conductor would be very hard to bend.
The diameter of the strands is a compromise between cost of manufacture (smaller wires require more manufacturing) and ease of installation. There is no particular reason for the exact size of the individual strands.
Without going into details on cable sizing calculations (there are entire national standards on this topic - see AS/NZS 3008 Electrical Installations - Selection of Cables.)
First, we decide what voltage we are using. In Australia, common voltages for distribution are 11, 22, 33kV; common voltages for transmission are 66, 132, 220, 300 kV. The higher the voltage, the thicker the insulation (XLPE) is required.
Secondly, we decide how much current-carrying capacity we need. We might, after some calculations, determine that the circuit needs to carry 100 amps, to satisfy demand in the present day, allow for future load growth, and a little bit extra capacity for contingencies. The more current capacity we need, the bigger the copper conductors need to be (mm².)
Thirdly, we determine what kind of environment the cable is going to live in. Current flow in a cable produces heat, and the current-carrying capacity of a cable is limited by its temperature. A cable installed in a hot environment can't carry as much current before it overheats, so we have to use a bigger cable than usual.
Knowing the voltage, current-carrying capacity, and installation environment of the cable, we are now in a position to select the size of cable required. We would do this by reference to a cable manufacturer's catalogue which has tables like this:
enter image description here Table reproduced from the Olex Australia HV Cable Catalog, 2009
As an example, I might decide that I need a 33kV cable that can carry 400 amps. It will be installed in underground ducts. I use the "current ratings" table to select the smallest possible cable that can carry 400 amps - in this case, a 240mm² cable would be required.
The nominal overall diameter of such a cable is 45.9mm.
Note that we don't really care about the 'diameter' of the cable as such - we care about the conductor cross-sectional area (mm²), i.e. how much copper is in the cable. The diameter only matters when you actually come to install the thing.
  • \$\begingroup\$ "There is no particular reason for the exact size of the individual strands." True for the cable in the picture you attached. The one in the question seems to be designed for AC and thus uses litz wire. The fact that the cross section looks like 6 sectors means that the wires in each sector are likely twisted. In this case, the size of the individual wires is determined by the skin depth. \$\endgroup\$ Commented Nov 24 at 22:46
  • \$\begingroup\$ @o3pw5a3k0rzh the cable construction in the original photo is "Milliken cable". It's designed to mitigate skin effect at 50Hz for exceptionally large cables. It's different than Litz wire in that the insulation is only between the six triangular sectors. The individual stands are not insulated from each other. The wires in each individual section are not twisted. Skin depth for copper at 50hz is 8.5mm so the size of individual strands is not relevant. \$\endgroup\$ Commented Nov 26 at 7:28
  • \$\begingroup\$ @o3pw5a3k0rzh on further reading, the construction of Milliken cable has more tricks than I thought. Some of the above may not be correct. \$\endgroup\$ Commented Nov 26 at 7:35
One of the responses in the Reddit discussion you linked said the cable could carry 69,000 to 500,000 volts, and this one would carry 1,000 to 1,400 Amps.
Large cables are normally composed of many smaller uninsulated strands - otherwise they would be too stiff to bend.
In normal 120/240 volt house wiring, AWG 8 and larger wires are stranded. In electronics, you may find wires as small as #26 stranded.
  • \$\begingroup\$ I understand the part about mechanical properties, but my point is more about what is the difference between a larger than optimal or smaller than optimal diameter, what a bad value for the diameter can cause and what are the properties and the facts to consider when choosing the diameter for a cable. Going back to my first question, so you are saying that this cable can drive up to 700,000,000 Watts ? What kind of electrical companies provide such Wattage ? It's huge. \$\endgroup\$ Commented May 22, 2014 at 20:13
  • \$\begingroup\$ @user2485710 Larger than optimal: more cost. Smaller: overheating, failure, leading to more cost. Electrical companies? Example: Drax. This cable would be a bad diameter for speaker wire. \$\endgroup\$ Commented May 22, 2014 at 20:50
  • \$\begingroup\$ 250KV - 500KV would be major transmission lines - a feed to a large city, certainly not a feed to an individual customer. My previous employer used a large amount of power - over 2 megawatts, if I recall correctly - and had its own substation, fed by a 69KV line. \$\endgroup\$ Commented May 22, 2014 at 22:04
  • \$\begingroup\$ ""What kind of electrical power companies provide such Wattage:" Any large power station - Loy Yang Power Station in Australia has a capacity of 3,150 MW just by itself. Any transmission utility - they carry that power to where it's used. \$\endgroup\$ Commented May 24, 2014 at 4:14