I'm sorry if this is an obvious question, but I've been scratching my head with it for a while.
I am used to UPS backup batteries that have an autonomy time between 2 to 4 hours, so I have always discharge tested for 3 hours down to a cutoff voltage of 1.8 Vpc. I have had issues going lower than that where batteries started to swell during recharge, although I think that in theory I could go down to 1.7 Vpc.
Recently started working on a datacentre with an autonomy time of 15 minutes. During the commissioning autonomy test the batteries discharged down to 1.83Vpc, and have been designed assuming an 8 year service life so will eventually drop down to 1.6Vpc. The manufacturer gives a 12 year life, but there are design factors for the fact the temperature is uncontrolled (!).
I have checked with the manufacturer who have told me that these batteries are OK to discharge lower, however some other people at work insist this will irreversibly damage all of the batteries without really being able to explain why. The manufacturer hasn't been so clear on why it is OK either, but they are a very large and reputable company.
My understanding has always been that a number of chemical reactions in a lead acid happen at a fixed rate independent of the rate of discharge, so that
- the amount of available energy is lower, so 1.6 Vpc at C0.25 is a lower % discharge than 1.6 Vpc at C3
- the equivalent change in internal resistance is lower, so although at C0.25 the internal resistance starts higher, over the course of 3 hours, the instantaneous i2r loss at a lower discharge rate may end up higher
My personal thoughts are that I tend to ask for a discharge test once every 3 years, and using a cutoff of 1.7 Vpc gives a decent margin of error. If they don't last for 8 years then that's on the designer's head.