We are using eGuage watthourmeters to monitor the outdoor unit on five VRF systems powered by two different 3P4W 120/208V high-leg delta panels. The neutral is not connected to the outdoor units.
We have connected the meters according to the manufacturer's instructions as shown in the diagram below:
We are satisfied that these are installed correctly and accurately metering the devices, however I'm struggling to understand how to interpret the current readings. Here's a sample of some of the readings we are seeing (one for each of the five units), including the angle between the current and voltage phasors (note that the eGuage only reports power factor, not leading or lagging -- I've converted it to degrees here):
Quantity [units] | Reading 1 | Reading 2 | Reading 3 | Reading 4 | Reading 5 |
L1 [V] | 120.8 | 120.8 | 120.8 | 120.8 | 120.8 |
L2 [V] | 211.9 | 211.9 | 211.9 | 211.9 | 212.1 |
L3 [V] | 120.7 | 120.7 | 120.4 | 120.4 | 120.4 |
S1 [A] | 10.658 | 15.574 | 23.364 | 12.067 | 12.871 |
S2 [A] | 15.337 | 19.767 | 26.674 | 15.757 | 17.057 |
S3 [A] | 11.866 | 15.711 | 22.992 | 12.661 | 12.805 |
|L1-S1| [deg] | 50.2 | 43.9 | 35.9 | 46.4 | 46.8 |
|L2-S2| [deg] | 21.6 | 19.9 | 16.3 | 22.9 | 21.7 |
|L3-S3| [deg] | 62.6 | 53.8 | 44.8 | 58.7 | 58.9 |
I found a Power Measurements Handbook which includes this phasor diagram for the distribution side of a high leg delta, to which I've mapped the labels of what we're reading:
The voltage is as I would expect. Assuming a purely resistive load, the angle between S2 and L2 should be zero. Then, the S3 and S1 currents lag their respective voltages by 30 degrees (just like in a delta). On the phasor diagram S1 appears to lead L1, because the reference direction (L1-N) is the reverse of the "normal" delta phase voltage.
What I can't explain is why the S2 current reading is higher than the other two. In my head it makes sense -- each leg is using an equivalent amount of current (call it x
), but the L1-L3 leg is split in half, so these two legs each use x + x/2
, while the high leg uses 2x
. This roughly matches what I'm seeing in terms of readings.
But is this correct? Mathematically, how can I determine what the three current measurements should be for a balanced high-leg delta load to verify what I'm measuring?