I am trying to size/validate the rating on the medium voltage main transformer for an industrial plant. For some reason I can't find many resources that indicate how to properly do this when you have mixed loads. Mixed loads meaning three-phase three pole, single-phase two pole, and single-phase one pole loads.
Suppose, for example, the transformer feeds a 3\$\phi\$, 4W panelboard with the following loads:
- (2) -- 100 A, 600 VAC, 3\$\phi\$, 3P
- (2) -- 50 A, 600 VAC, 1\$\phi\$, 2P
- (2) -- 15 A, 347 VAC, 1\$\phi\$, 1P
What is the proper way of determining the supply transformer rating?
My thoughts/work:
- I could simply calculate the apparent power using both the three-phase and single-phase formulas and add them together. Resulting in:
$$ S_{TOTAL} = \sqrt3 * 600 V_{LL} * 200 A + 600 V_{LL} * 100 A + 347 V_{LN} * 30 A = 278 kVA$$
- I could also recognize that the legs need to be distributed in the panelboard -- the three-phase load will be added to all phases, but single-phase loads can't be split up evenly. Resulting in:
$$ S_{TOT} =99.3 kVA * 3 = 297.9 kVA $$
- Neither of these items take into account standard transformer sizing, derating, power factor, demand factor, or allowable loading.