I'm working on a small LVDC project using 60 VDC to distribute power over varying distances to varying loads such as network equipment. I decided to work out the maths and see exactly how much power I can get (maximum) over specific distances.
For this specific case I am assuming AWG14 (\$2.5\rm\, mm^2\$) cable is being used.
The voltage drop over the cable will be:
$$V_{drop} = I_{wire} \cdot R_{wire}.$$
The voltage available at the load will be:
$$V_{load} = V_{supply} - V_{drop},$$
which is equivalent to:
$$V_{load} = V_{supply} - \left( I_{wire} \cdot R_{wire} \right).$$
Resistance of a wire is
$$R_{wire} = {2 \cdot L_{[\rm m]} R_{wire[\rm\Omega/km]} \over 1000\,\rm m}. $$
Re-writing:
$$V_{load} = V_{supply} - I_{wire} {2 \cdot L_{[\rm m]} \cdot R_{wire[\rm\Omega/km]} \over 1000\,\rm m}.$$
Power will be given by voltage at the load times current in the wire. Voltage supplied in this case is 60 V so the resulting expression for power at the load can be written:
$$\begin{aligned} P_{load} &= \left( 60{\,\rm V} - I_{wire} {2 \cdot L_{[\rm m]} R_{wire[\rm\Omega/km]} \over 1000\,\rm m} \right) \cdot I_{wire} \\ &= 60{\,\rm V} \cdot I_{wire} - I_{wire}^2 {2 \cdot L_{[\rm m]} \cdot R_{wire[\rm\Omega/km]} \over 1000\,\rm m}. \\ \end{aligned}$$
I am looking to maximize the power available at the load with respect to the current in the wire - so using partial differentiation:
$$\begin{aligned} {\partial \over \partial I_{wire}} P_{load} &= 60{\,\rm V} - 2\ I_{wire} \cdot {2 \cdot L_{[\rm m]} \cdot R_{wire[\rm\Omega/km]} \over 1000\,\rm m} \\ &= 60{\,\rm V} - 4\ I_{wire} {L_{[\rm m]} \cdot R_{wire[\rm\Omega/km]} \over 1000\,\rm m}. \\ \end{aligned}$$
To maximize, set the derivative to zero and solve - yielding:
$$ I_{wire} = {15000 \over L_{[\rm m]} \cdot R_{wire[\rm\Omega/km]} }. $$
So for example, at 50 m with a wire resistance of 14 AWG as \$ 8.286 \, \Omega/{\rm km} \$:
$$ I_{wire} = {15000 \over 50 \cdot 8.286 } = 36.3 {\,\rm A}. $$
At this current, the maximum power is achieved. The voltage drop with this current can be calculated to be approx. 30 V, so the power delivered would be just over 1 kW at 1086 W.
Obviously 36.26 A is a lot of current especially for 14AWG so I would cap this at a much lower level or use 3 cables to divide the current by 3.
30 V at the end of the cable can then be stepped-up or down depending on device. So taking around 10-15 % losses in efficiency for the DC/DC converter - around 900 W can be transmitted at 60 VDC over 50 m.
I want to expand this to longer distances such as 200 m, 300 m and maybe further. Just want to check my thinking/maths is correct as it may be useful for someone else who may come across the same question.