How can I calculate the current carrying capacity of a DC copper bus bar with respect to temperature?
Bus bar specifications:
Width=40mm
Thickness=6mm
How can I calculate the current carrying capacity of a DC copper bus bar with respect to temperature?
Bus bar specifications:
Width=40mm
Thickness=6mm
The permitted and the practical loading of busbars is a complex matter taking into account much more than just the resistivity of the material. I suggest reading the industry association's (free) comprehensive monograph on this topic:
Chapter 2 covers current carrying capacity and its calculation, which depends on many complex factors including the skin effect depth, bar shape and spacing, cooling mechanisms and so on.
There are two design limits; the maximum permitted temperature rise, as defined by switchgear standards, and the maximum temperature rise consistent with lowest lifetime costs - in the vast majority of cases, the maximum temperature dictated by economic considerations will be rather lower than that permitted by standard.
...
Lowering the temperature by increasing the size of the conductor reduces energy losses and thereby reduces the cost of ownership over the whole lifetime of the installation. If the installation is designed for lowest lifetime cost, the working temperature will be far below the limit set by standards and the system will be much more reliable.
As you would expect, the exact kind of copper affects resistivity a lot, and there is good coverage in the book on the effects of different impurities and alloys. They say "normally, the purest copper is used for bulk conductors".
If you just want the basic effect of temperature on resistivity, the give a formula for basic resistivity of high conductivity copper for temperatures up to 200°C (section 1.2.2.1.1) as
R = R20(1 + α20ΔT)
After a lot of searching, the best source I found was an old german DIN standard from 1975. https://www.sis.se/produkter/elektroteknik-24c2329a/elektriska-linor-och-kablar/linor/din43671/
However, rittal have incorporated the information from this in english and a more modern format in their catalogues. One which you can find below. https://www.rittal.com/imf/none/3_1978/
Following this standard you can find that Barsize: (40; 5)m m bar' Bar coating: none, bare bar Ambient temperature: 35 ce Bar temperature: 65 ce Continous current: 484 A DC