I was attempting to help out in this question here regarding calculating instantaneous three-phase power values which allows for numerical or real-time calculation of unbalanced and arbitrary loads. Calculating 3-phase real and apparent power using sampled signals

However, we ran into a complication in that if a arbitrary, potentially unbalanced delta load is assumed then we cannot derive the phase currents from the measured line currents, while for an arbitrary, potentially unbalanced wye load we cannot derive the phase voltages from the line-to-line voltages.

After failing to find a solution to derive equations for either delta or wye using three voltage and three current measurements, I had to search around and found Blondel's Theorem which requires two meters where the equations just happen to magically from the measurements simplifies down the sum of the instantaneous phase power in a wye with a neutral (voltages taken with respect to the neutral): $$p(t) = \sum_{\phi =a,b,c}v_\phi(t)i_\phi(t)$$

I have been unable to find how to calculate instantaneous three phase power outside of Blondel's Thereom and outside of a Wye with a neutral point (since you have direct measurement of all phase voltages and currents in that case so it's easy).

My question is how was instantaneous three phase calculations actually performed before Blondel? Particularly if the source could be not be assumed to be balanced? From where I am sitting I can't see a way outside of just having a wye with a neutral. If that were true, that would mean that in order to measure the instantaneous power there has be a at least one wye with neutral somewhere, either load or source. That might not be a problem if you're a utility since you can always choose to supply using a wye with a neutral but also means you're stuck if you're a user without access to the utility neutral or without a wye with neutral load.

EDIT: I suppose if you knew the source was balanced and had no access to the neutral then you could synthesize the neutral with three resistors to obtain neutral-referenced voltages (or just \$\sqrt 3\$) and calculate the power from the source side. And I guess the same approach could be done with a delta source. But these rely on the source being neutral. So even this is true, what do you do when the source is not balanced?

\$\endgroup\$
3
  • \$\begingroup\$ I don't know about calculations but for measurements, the two-wattmeter method has been used since before god was a kid. \$\endgroup\$
    – Andy aka
    Commented Feb 24, 2022 at 9:27
  • \$\begingroup\$ PQ theory? You would need to sample the three LN voltages plus currents. Then obtain alpha-beta quantities with which you can construct P and Q. So it doesn't require neutral. \$\endgroup\$ Commented Feb 24, 2022 at 9:27
  • \$\begingroup\$ @aconcernedcitizen "You would need to sample the three LN voltages plus currents." Doesn't that defeat the purpose? And I have to look into it but at a glance it doesn't seem to be truly arbitrary in that it wouldn't say work with a VFD as a load or source that is not periodic and also not steady state. Or if you had a case where different loads were being added or removed while operating. \$\endgroup\$
    – DKNguyen
    Commented Feb 24, 2022 at 14:36

1 Answer 1

2
\$\begingroup\$

No doubt someone will give a better answer, and if this does not fit your requirements, feel free to downvote, but to my knowledge the PQ theory is successfully used in active power filters for both unbalanced and harmonic content conditions. The DQ theory may be more suited to VFDs give the control of the motors, but if it's about the calculation of powers, it can be done in 3 wire systems by using these equivalences (using Akagi's PQ theory):

$$\begin{align} v_a&=v_{ab}-v_{ca} \tag{1a} \\ v_b&=v_{bc}-v_{ab} \tag{1b} \\ v_c&=v_{ca}-v_{bc} \tag{1c} \end{align}$$

With these you can then proceed to calculate the \$\alpha\beta\$ components:

$$\begin{bmatrix} v_{\alpha} \\ v_{\beta} \end{bmatrix} =\sqrt{\dfrac23} \begin{bmatrix} 1 & -\dfrac12 & -\dfrac12 \\ 0 & \dfrac{\sqrt3}{2} & -\dfrac{\sqrt3}{2} \end{bmatrix} \cdot \begin{bmatrix} v_a \\ v_b \\ v_c \end{bmatrix} \tag{2}$$

The same for currents. The powers will then be:

$$\begin{bmatrix} p \\ q \end{bmatrix} = \begin{bmatrix} v_{\alpha} & v_{\beta} \\ v_{\beta} & -v_{\alpha} \end{bmatrix} \cdot \begin{bmatrix} i_{\alpha} \\ i_{\beta} \end{bmatrix} \tag{3}$$

The resulting powers will have both DC and oscillating values:

$$\begin{align} p&=\bar{p}+\tilde{p} \tag{4a} \\ q&=\bar{q}+\tilde{q} \tag{4b} \end{align}$$

As far as active power filters are concerned, there are many strategies, but for a more common shunt APF, constant power strategy, \$p\$ is filtered of its DC component and negated, $q$ is negated, and to these two there is an additional power called "loss power" coming from the DC bus regulation which is added:

$$\begin{bmatrix} i_{C\alpha} \\ i_{C\beta} \end{bmatrix} =\dfrac{1}{v_{\alpha}^2+v_{\beta}^2}\cdot \begin{bmatrix} v_{\alpha} & v_{\beta} \\ v_{\beta} & -v_{\alpha} \end{bmatrix} \cdot \begin{bmatrix} -\tilde{p}+\bar{p}_{\text{loss}} \\ -q \end{bmatrix} \tag{5}$$

Finally, the inverse Clarke is applied, and the currents are used for comepnsation:

$$\begin{bmatrix} i_{Ca} \\ i_{Cb} \\ i_{Cc} \end{bmatrix} =\sqrt{\dfrac23}\cdot \begin{bmatrix} 1 & 0 \\ -\dfrac12 & \dfrac{\sqrt3}{2} \\ -\dfrac12 & -\dfrac{\sqrt3}{2} \end{bmatrix} \begin{bmatrix} i_{C\alpha} \\ i_{C_\beta} \end{bmatrix} \tag{6}$$

A proof of concept can be simulated in SPICE. While I could show an exploded view with all the gory details, I'd say a schematic at block level can be read much better.

There are a few shortcuts I used, mostly for the sake of space, to be able to show al the schematic at once. The voltages are directly measured against a some common point, nul, but here they represent (1a,b,c), which still stand:

(1a, 1b, 1c)

[EDIT] Note that the upper graph shows a grey label but an orange trace. That's the result of a .STEP, which has one of the traces (grey) as being null, and the other (orange), non-null. If you zoom in you'll see that the X axis is a slightly lighter shade of grey than the Y axis, when they should be the same -- that's the zero valued first trace. The exaplanation is at the end edit. [/EDIT]

Then, I used some emulated NTC, which is also deleted from the final schematic, but the currents will show a gradual rise. Lastly, the formulas above are for a constant power strategy, but I'm showing a sinusoidal current strategy, that's why you'll see a Clarke transform for the currents which is not used and, instead, some unity sine/cosine are used; the purpose was a better viewing of the graphs.

APF, sinusoidal current strategy

Ug is the grid (up, left), feeding two nonlinear loads: two bridges, one with a parallel RC (usual rectifier, 3 phase), and one with a series RL (but only on two phases). In the lower side there are the isolated voltage sensors [consider them (1a,b,c)], the Clarke matrices for both currents and voltages (2), calculation of powers (3) [with the modification mentioned above], selection of powers (ignore the i_zero, it's null), calculations of compensating currents in the \$\alpha\beta\$ domain (5), inverse Clarke (6), feeding the compensating currents back into the grid through the Ga, Gb, Gc current sources.

APF waveforms

[EDIT 2] I forgot to post this last time, but the loads have changed to the regular bridge + R||C that you see, plus a simple series RL connected between phases a and b. Ultimately, it doesn't matter, the purpose was to have a nonlinear load and an imbalanced load, and to see how the PW theory works. [/EDIT 2]

Plotted are (top to bottom): powers calculated before and after the point of common coupling (PCC nodes), the output currents, the input currents, and the LL voltages showing unbalance (V(a) is 0.8 pu) and harmonics. At 96 ms the APF turns on, showing clean sinusoidal currents on the input side. If the power strategy would have been used, the currents would have still had harmonics (though greatly reduced), while the input power would have been flat:

power strategy


As per the comments below, (1) might not be intuitive, so here's why it holds (there's a typo in the 2nd comment, 2 instead of 3):

$$\begin{align} \sin(x+\theta)&=\cos(\theta)\sin(x)+\sin(\theta)\cos(x) \tag{7a} \\ \sin(x-\theta)&=\cos(\theta)\sin(x)-\sin(\theta)\cos(x) \tag{7b} \\ (7a)+(7b)&=2\cos(\theta)\sin(x) \tag{7c} \\ v_{ab}&=v_a-v_b \\ v_{ab}-v_{ca}&=v_a-v_b-(v_c-v_a) \\ {}&=v_a-v_b-v_c+v_a \\ {}&=2v_a-v_b-v_c \tag{8} \\ v_a&=\sin(x),\;v_b=\sin(x-\dfrac23\pi),\;v_c=\sin(x+\dfrac23\pi) \\ (8)&=2\sin(x)-2\cos(\theta)\sin(x)\Biggr|_{\theta=\frac23\pi} \\ {}&=2\sin(x)-2\cdot\left(-\dfrac12\right)\sin(x) \\ {}&=3\sin(x) \tag{9} \end{align}$$

These relations hold only as long as there is no imbalance. But -- and here is the key -- the Clarke transform cancels the zero component, which is not needed in a 3-wire system. This is why you can see a non-zero trace in the upper plot of the 1st picture (orange), versus a zero valued one for the other (grey, overlayed on the X axis).

To further prove this, in the previous pictures the generator is disposed in Y, even if the common (the NUL pin) is clearly connected to a capacitor in parallel with a 1 MΩ resistor (and a series 1 Ω to limit the potential currents) -- it is floating. So, this time, here is a Δ generator, and how the waveforms look like before and after the Clarke matrix, for each (note the imbalance in V4):

Delta generator

The bottom plot shows the LN voltages, referenced to the SPICE ground (ugly, meaning the voltage across C7 will not be zero), the middle shows the derived voltages, and at the top there are the resulting currents for a constant power strategy -- showing that the scheme works. I've left the αβ components separate, for better viewing:

Clarke for Delta generator

Here, too, the zero component is non-null, but this time it's on the abc side, since they are derived from Δ, not Y.

So, as a conclusion, it doesn't matter how the derived abc come out, the Clarke matrix and the subsequent power calculations will correctly account for the 3- or 4-wire system, since the purpose of the Clarke matrix is to consider the three-phase as a whole, not as individual, summed components.

\$\endgroup\$
7
  • \$\begingroup\$ If equations 1 are true, that seems to be all you need to weed out the neutral referenced voltages from line-to-line measurements for an arbitrary 3-phase load or source so should work for a neutral-less wye. Not obvious to me why it would be true glancing at a wye though. \$\endgroup\$
    – DKNguyen
    Commented Feb 24, 2022 at 18:52
  • \$\begingroup\$ @DKNguyen I see now that I forgot to mention something, even if it is in the 1st picture. The zero components are different (top plot): for the regular abc voltages, the zero component is non-null (orange), while for the derived method, it is (I stepped a value and you can see that the label is grey, while the plot is only orange, and the 1st stepped waveform, because it's zero, it's mistaken with the X axis). It makes sense, since it's a 3 wire system, but it's not clear from the plot. But if they are different it's only because of the imbalance. \$\endgroup\$ Commented Feb 24, 2022 at 19:05
  • \$\begingroup\$ Also, the equations make sense if you consider that Vab=Va-Vb, so Vab-Vca=Va-Vb-(Vc-Va)=Va-Vb-Vc+Va=sin(x)-sin(x+2/3*pi)-sin(x-2/3*pi)+sin(x)=2*sin(x). Hm, now I see I also forgot the scaling, but you can see it in the 1st picture. \$\endgroup\$ Commented Feb 24, 2022 at 19:11
  • \$\begingroup\$ Equations (1) aren't checking for balanced or unbalanced out unless Va, Vb, and Vc are not supposed to be neutral referenced voltages but something else. Falstad Simulator: tinyurl.com/y7hb4u2f \$\endgroup\$
    – DKNguyen
    Commented Feb 24, 2022 at 22:54
  • \$\begingroup\$ @DKNguyen They do, see my 2nd comment: after the Clarke matrix the zero component is non-null for derived equations when there is imbalance, but it can be discarded. You can clearly see that the results are the same. The change was made for the constant power strategy (hence the slightly distorted current), but the currents overlap. Also, what you're showing seems to be just a summing of the three voltages, not a Clarke matrix. \$\endgroup\$ Commented Feb 25, 2022 at 9:47