Today, electronic systems use constant voltage power source. Current consumption varies as power consumption varies. Why can't electronic systems be designed the other way round? Using constant current power source and varying the voltage as power consumption varies. What are the pros and cons of each approach? Why has current electronic systems evolve to use constant voltage power source?
1\$\begingroup\$ Voltage and time are only indirectly related, whereas current and time are directly related. \$\endgroup\$– Ignacio Vazquez-AbramsApr 9, 2017 at 12:39
1\$\begingroup\$ Most circuits require a varying amount of current (e.g. audio amp) - much easier to supply a voltage and then take just the current required than a current (which would have to equal the maximum value required) and then have to dump the excess current not required as wasted power. Besides most sources of power are 'constant' voltage e.g. battery \$\endgroup\$– JIm DeardenApr 9, 2017 at 12:41
2\$\begingroup\$ This is very closely related to your electronics.stackexchange.com/questions/298564/… question - please don't ask a succession of similar questions. \$\endgroup\$– TonyMApr 9, 2017 at 12:55
10\$\begingroup\$ Work through the examples yourself and it becomes clear enough. A CCS outlet must be shorted when unused or voltage will rise to infinite (or system max.) Multiple devices from a single output must be placed in series. Power will be lost on the feed circuits at all times at the same level regardless of load due to I^2R losses. If voltage is limited due to safety or other uses the CC must be increased for higher power ccts. While available outlet max power rises linearly with I, constant losses rise with I^2. | Overall it IS possible but gets nasty. \$\endgroup\$– Russell McMahon ♦Apr 9, 2017 at 14:10
3\$\begingroup\$ @IgnacioVazquez-Abrams voltage and time are just as directly related as current and time if you work fully through to the dual system, ie inductance for capacitance, inductors charged with current are current sources and have a maximum volt.second product, just as capacitors charged with voltage are voltage sources and have a maximum current.second product. \$\endgroup\$– Neil_UKApr 9, 2017 at 15:10
Most power sources are constant voltage, and not constant current. If you take the two main sources of electrical energy, which are batteries and rotating generators(regardless of size), the one thing in common is that their voltage is fixed theoretically to a certain value and can be controlled. For example, a standard AA dry-cell battery has a voltage of 1.5 V, which it will always produce more or less (disregarding real-life errors). The internal chemistry of most batteries relates the internal chemical reactions to the output voltage of the battery. Similarly the generator, for a given magnetic field strength (called excitation), and a given speed, will produce a fixed voltage at its terminals(again, only approximately due to real-life).
In almost any electricity-using device, in almost most cases, a voltage is the cause, and the current is the effect. Only when you apply a voltage to a device, may current start flowing through it (superconductors not-withstanding). Even constant current devices monitor the current and regulate the voltage as per the load. You never hear of a 3 V flashlight battery monitoring the voltage at its terminals. This is due to basic physics, in which change in movement of electrons (i.e. current) is possible when electric field (i.e. voltage) is applied.
5\$\begingroup\$ "In almost any electricity-using device, in almost most cases, a voltage is the cause, and the current is the effect." - because they were designed that way. The question is asking why they were designed that way. \$\endgroup\$ Apr 10, 2017 at 1:19
4\$\begingroup\$ Voltage and current are two faces of the same coin (even though it is sometimes easier to regard one as the cause and the other as the effect, there is no physical reason for that). Even in a battery - the exemplification of constant voltage source - once a current is flowing ("due to the voltage", the only way to maintain the voltage is to route charge back to the battery to re-estabilish the equilibrium between ions. So, that voltage is actually "due to the current". What is usually overlooked is the fact that each single little charge carries a field that would otherwise change the voltage. \$\endgroup\$ Apr 10, 2017 at 3:29
2\$\begingroup\$ @TransistorOverlord, point is that voltages do not appear from nowhere. They are created by displacing charges. Two sides of the same coin. Related question: electronics.stackexchange.com/questions/201533/… \$\endgroup\$ Apr 10, 2017 at 4:21
2\$\begingroup\$ @TransistorOverlord Indeed batteries are approximate constant-voltage devices and I've never heard of a constant-current battery. But I believe there are configurations of generators that are closer to constant-current than constant-voltage (which makes sense because motors are also inductors). Perhaps there are configurations in which chemical reactions can be made to generate a constant current too. \$\endgroup\$ Apr 10, 2017 at 4:25
2\$\begingroup\$ @TransistorOverlord A solar cell, for example, approximates both a constant current source (up to a certain voltage limit) and a constant voltage source (up to a certain current limit). (In practice you use an MPPT circuit to operate it in-between, and by altering the MPPT circuit you could get either a constant-current or constant-voltage output) \$\endgroup\$ Apr 10, 2017 at 4:47
While there's no reason why you couldn't design electronics with constant current sources, there's a few good reasons why we don't. Batteries and mains power are supplied more as constant voltage sources than constant current sources so it's simply more convenient to use what we have. The other reason is that a constant current source is always burning power. To shut a device off, you would have to short-circuit the power-supply. Since most wires have resistance, you'd constantly be wasting power.
7\$\begingroup\$ For the second part, I guess it all boils down to the fact that (almost) perfect insulators are cheaper and easier to come by than (almost) perfect conductors. \$\endgroup\$ Apr 10, 2017 at 3:16
The constant voltage method provides the key to load-line design of amplifiers.
Given the vast need for amplifiers, the ability to provide stable gain for boosting long-distance phoneline signal strengths, the need for low distortion operation of vacuum tubes in those phoneline circuits, we may feel hobbled by the successes of BellLabs. But then Bell provided the transistor. Here is a load-line.
Such systems are in use in LED lighting applications (LEDs behave exactly like your question suggests natively), and they also were very relevant in the last decades of widespread vacuum tube technology (50s,60s,70s) - 300mA and 150mA series heater designs (which, however, were usually manually adjusted with resistors instead of using a proper regulated current source) were very common in consumer equipment.
You are thinking about voltage and current as a more closely related thing than they actually are. Voltage is a "static" potential. Current on the other hand is the motion of charges due to the effect of a voltage. For a given load in a circuit they are related by ohm's law, but they are physically different entities.
A voltage can, and does, exist when there is no current present. However, other than at absolute zero, a current can not exist without a voltage.
That is, Voltage is the primary object, current is the secondary.
Some circuits ARE designed to be powered by a constant current source. Many transducers like motors and LEDs are driven that way because their energy conversion characteristics are dependent on current, not voltage. However, it is important to note that constant current sources are controlled by voltage effects.
However, most electrical parts have characteristics that are fundamentally affected by voltage, especially capacitors and the conductance of semi-conductors. As such it is a lot easier to implement complex circuitry using a constant voltage supply and allow the current consumed to vary as it may.
Were you to try and build the same sort of circuitry using a constant current power supply, when one part of the system demands more power, it's resistance drops, the voltage would need to fall system wide to maintain the same current output from the regulator. This would change the references for all the remaining circuitry and affect how the capacitances and semiconductors behave in them. If it falls too low some semi-conductors would stop working.
As such, your constant current source would need to be designed to be at least your maximum system load.
Now you have the opposite problem. If that load dropped to a much lower level because you turned something off, your circuit resistance would be much larger, and so your system voltage would have to grow to a much larger value. All your components would need to be designed to deal with those larger voltages. If it goes too high your semiconductors again may suddenly stop working.
Further, if you had an ideal constant current source, as your load approaches a very high resistance, the voltage starts to approach infinitely. At which point physics takes over, insulators fail, and everything would self destruct. In reality what would actually happen would be the regulator would no longer be able to supply the current because it does not have the voltage to draw from to drive the output that high.
The alternative to that would be to not turn things on and off but to redirect it elsewhere instead, which, as well as being a waste of energy, is also extremely difficult to do while maintaining a constant total current. Further every little logic gate and amplifier would need do to the same thing.
In a constant voltage system each circuit contained within it is, to the most part, immune to what other parts of the system are doing. If a circuit on the right side of the board suddenly draws more current, and the regulator can supply it, and the board is designed correctly, the circuit on the left side is blissfully unaware of it. (Well almost.)
The bottom line is, in almost all cases, voltage, being the prime mover, is the thing that makes most sense to regulate and is a lot easier to control.
1\$\begingroup\$ And you are thinking about voltage and current as less closely related than they actually are. Most circuits can be converted into an equivalent circuit with current and voltage interchanged. \$\endgroup\$ Apr 10, 2017 at 1:17
\$\begingroup\$ @immibis no I mean, drawing more current does not mean you need more voltage as the OP's original question suggests. \$\endgroup\$– Trevor_GApr 10, 2017 at 1:21
\$\begingroup\$ To get more power from a constant-current power supply, you don't draw more current (you can't, because the current is constant). Instead you develop more voltage, which increases the total power delivered since the current stays the same. \$\endgroup\$ Apr 10, 2017 at 1:23
\$\begingroup\$ @immibis if you change power yes.. I may have missed that point. \$\endgroup\$– Trevor_GApr 10, 2017 at 1:29
1\$\begingroup\$ @Trevor, I believe you are not considering one aspect when you say "A voltage can exist without a current present". I.e. the fact that you must have displaced charge to produce that voltage in the first place. Also, if you are willing to consider perfect insulators (that allow for any value of V to be associated with the particular value I=0), you should also consider perfect conductors (that allow for any value of I to be associated with the particular value V=0). Granted, it is easier to think that a gradient of potential energy is causing a small mass to move in a give direction; but... \$\endgroup\$ Apr 10, 2017 at 4:46
Lets imagine two outlets on a common house plug, fed by a constant current source somewhere further up the line, lets assume it's a 10A constant current source. When not in use the outlet needs to be shorted such that the voltage is zero (lets assume ideal wires for now). When you plug something into one outlet, you now need to un-short it, and allow the voltage to rise - lets assume you have a 10V 10A -> 100W lightbulb plugged in, and the act of plugging it in moves the short-circuit system out of the outlet. Now what happens when you plug in a second 100W lightbulb (10A, 10V) - the lightbulb now needs to function at 5A 20V - it needs to lower it's own resistance - and so does the other one - but how much? well it depends on the other device that was plugged in - the two basically need to stabilize, which while possible, is a very complicated system for a device as basic as a lightbulb, not to mention the special socket that would be needed to short closed when all devices are removed. This sort of current-voltage balancing system would need to be done for every splitter, leading to some complicated systems that need to balance themselves.
Now, I was ignoring wire resistance, but lets bring it back - you will always be running your wires at their maximum (since wires are rated by amps running through them for the most part) - this is not ideal, as using something at 24x7 to it's maximum is generally not good for it's lifespan, so you will need to increase the size of all the wiring to support this. Beyond the wiring you will also need to be able to quickly and reliably switch at 10A currents - 10A is a fair amount of current, which ends up causing sparks / arcing, thus wearing out switches fairly quickly, which brings me to another point.
Right now most mains power is AC, in that it has a zero-crossing - but you won't be able to instantly change 10A of current into -10A due to wire (and device) inductance. Large appliances can adjust their "power on" time to the frequency of the mains power, such that their switches (or relays / mosfets / whatever) turn on when the voltage is at or near 0, in order to prevent surges into say a capacitor bank that then feeds the system during the next 0V cycle. While I won't say that this is impossible, it would be quite difficult at best.
2\$\begingroup\$ No, the two lightbulbs would be connected in series, and both would operate at 10A 10V (the supply from the outlet now being 10A 20V). \$\endgroup\$ Apr 10, 2017 at 1:17
\$\begingroup\$ You can't instantly change 10V of voltage into -10V due to wire (and device) capacitance, but that doesn't mean we don't use AC voltage. \$\endgroup\$ Apr 10, 2017 at 1:18
\$\begingroup\$ @immibis connecting the devices in series adds it's own complexity, meaning each device needs to handle the power of all other possible devices, or they go out like Christmas lights - I suppose there could be a sine wave of current, but with devices already modulating their resistance to get their desired power I am not sure how effective it would be \$\endgroup\$ Apr 10, 2017 at 2:07
\$\begingroup\$ Yet you don't see a problem with a sine wave of voltage and devices modulating their resistance to get the desired power? \$\endgroup\$ Apr 10, 2017 at 2:09
\$\begingroup\$ And with a constant current supply, connecting devices in series is the only way to sanely connect multiple devices. Just like with a constant voltage supply you have to connect them in parallel. You've already alluded to this with the fact that powerpoints would have to be shorted when not in use. \$\endgroup\$ Apr 10, 2017 at 2:15
I think most other answers point out the real issue only rather tangentially. It would work but be rather thoroughly impractical for very basic reasons, even ignoring the whole problem of generation and distribution when the end-users would be constant-current loads with compliance of thousands of Volts for home users, and good fractions of a megaVolt for larger users such as shopping malls, etc.
Why can't electronic systems use constant current power source and vary the voltage as power consumption varies?
They can, but the reciprocal relationships between related quantities make it totally impractical for power distribution, even at the level of a house. Also: it solves no practical problems whatsoever. No improvement of any kind. In fact, even with the most careful design, the system would be extremely expensive to implement, even at the scale of a household.
Constant voltage power can supply multiple loads in parallel, like you do with typical household electrical wiring. When a load is turned off, the conductance drops to zero, and no more current flows. The capacity of a supply, at a constant voltage, is given in Amperes.
Constant current power supply would require all loads to be connected in series. When a load is turned off, the resistance drops to zero, and the current bypasses the load. The closed switch maintains a short on the input. The capacity of a supply, at a constant current, is given in Volts.
With constant-current supply, the house wiring would be one big series circuit, and each outlet would need to bypass the contacts with a short whenever the load was not plugged in. All loads would need to conduct the full current consumed by the household, since all the power switches turned into the "off" position would have to have zero (very low) resistance so as not to dissipate power.
Since the capacity is equivalent to maximum voltage, upgrading a house supply capacity would mean getting higher maximum voltage fed to the outlets. Let's say that a practical constant current for household use would be 15A. A rather standard 24kW household supply - US 240V/100A house service - would become a "medium" voltage 1.6kV supply. A 200A service for larger homes would take 3.2kV line voltage.
Also, the static idle dissipation of a household would be proportional to the number of outlets, and to the square of the current since all the wiring and outlets would have some resistance, and \$P=I^2/R\$.
So, if you'd "turn off" everything in the house, the electricity meter would not stop. To actually stop the electric consumption, you'd have to short the supply side of the electric meter.
The only "cool" aspect of such a supply, ignoring the insane risk of electrocution, would be that short circuits would be completely benign. A hard short circuit in an appliance would be equivalent to turning it off :)
Also, "fuses" in appliances would need to monitor both voltage and current. So, you'd have a regular 25A fuse, and behind it an equivalent of crowbar circuit that shorts the input in case the voltage is above a threshold. The crowbar would need to use a 25A, 5kV-rated relay to cover "household" power delivery ranges expected.
Now, the relays would need to have a very small interrupting capacity - and so would the fuses - since the supply is inherently current-limiting. But they'd need to support insane standoff voltages.
The tiny catastrophic protection fuse (or fusible resistor) in a phone charger would instead consist of a $50 fuse, and a $100 relay...
Don't know about you, but I wouldn't be happy to pay for this, even with all the "cool engineering beans" factor.
