The situation I will describe is in a rural property that recieves only one wire from the power grid at 13.5kV. We have a single phase 25kVA transformer, that is shared with another house. On the primary side, one of the leads is connected to the wire from the power grid and the other to earth. On the secondary side is the standard 240V/120V 3 wire split-phase connection.
The problem encountered is that with almost no load (at the time of the testing I checked the neighbors electric meter and it only reported only 300W) the ground to to neutral voltage is 10V, one line to ground voltage is 130 and on the other line it's 110; note that the voltage between both hot wires is 240 and between each hot wire and neutral it's 120v. When a heavy load is aplied, we tested connecting a 4500W 240V water heater, the voltages were N-G:50V, L1-G: 170V, L2-G:70V and when the voltage between the ground of the circuit and an improvised ground was 5V. The measurements where taken both at the electric panel that is imediate to the electricity meter and on an electric socket inside the house. The values I wrote are rounded, as expected the L1-L2 voltage droped a small amount when the heater was on.
My conjecture based on the behavior of the voltage dependant on load and visual inspection of the wiring of the tranformer is that the same ground connection used for the primary side is used to ground the secondary side neutral and that the connection to ground used has a relatively high impedance. Those two things combined mean that the ground connection with too much impedance causes the IR voltage drop in the conductor between the transformer primary side neutral lead to the ground rod to be affecting the secondary side neutral voltage with respect to ground. The L1-L2 and L1,L2-N voltages are okay, even though the L1,L2-G and N-G voltage are dangerously wrong since the neutral to ground voltage is in phase with one of the lines and out of phase by 180º with the other line. Another important detail is that the electrician connected the house's circuit ground to the ground rod used for the transformer, wich explains why the circuit ground to improvised ground voltage was 5V when under load.
I wanted to ask here to know if my reasoning is posible or if there is some other explanation for the problem, since we contacted the electricity company and they have only, for the momment, sent an electrician and got nowhere, since they measured the L1-L2 and L1,L2-N voltages and saw they were okay and before they could do any further testing the electricity went out, so they had to leave (on that zone the electricity company has programmed blackouts, 6 hours of power/6 hours without power).
So you have a pretty standard SWER setup. Turns out because SWER is considered "low-cost", local electricians tend to build it "even lower cost" and skip the secondary grounding. Like this:
From what you described, my bet is the shared ground rod is simply too small or too rotten or the earth humidity is too low. The reason why the phases on the secondary behave differently is because the secondary current is in phase or in counterphase with the primary ground current.
The problem with this shared ground rod is, the grounding needs are different for the primary and secondary.
The utility company electricians (who I expect they know what they are doing) installed a primary ground rod for a constant current of a few amperes, and a loss of a few dozen volts from 10kV doesn't matter much. So, primary grounding doesn't give you headaches. A small rod suffices, even in dry earth.
On the secondary, you don't have a constant ground current of a few amperes, but instead, you want to have a ground fault current of a few thousand amperes which should trip the breaker immediately. Three problems with the above setup arise:
  • The primary grounding is built much too weak for these ground currents. You will have a lift of the neutral to the 10kV level in case of ground fault. This can break even more insulations on the secondary. Random appliances in the house may be broken after a ground fault.
  • The ground fault current may damage the primary ground rod, which isn't made for currents of thousands of amperes, not even for a second.
  • The breaker may not trip because of the above two problems.
    \$\begingroup\$ All the poor Earthworms from point A to point B... \$\endgroup\$
    – rdtsc
    Commented Jan 9, 2019 at 0:29
  • \$\begingroup\$ The effect of such an operational grounding is within a few metres for the low currents we are talking about. And it's AC. Tramway operational grounding is a real challenge. Crossing iron pipes in the ground just rust away if you do it wrong. \$\endgroup\$
    – Janka
    Commented Jan 9, 2019 at 0:33
  • \$\begingroup\$ So having the electricity company install a better grounding rod with a low resistance connection to the soil wil fix the issue? Should they install independant rods for each side of the tranformer or will it work fine the way it is connected with just a better ground connection? \$\endgroup\$
    – JABN
    Commented Jan 9, 2019 at 23:06
  • \$\begingroup\$ First, you should try to fix the problem by watering the ground around the grounding rod. Make it a swamp. If that's not possible because of the winter, you could add additional grounding rods, preferably near your house. A ten meters long trench with a steel band in it should do the trick. Keep it all as wet as possible. \$\endgroup\$
    – Janka
    Commented Jan 9, 2019 at 23:12
  • \$\begingroup\$ I will try watering the soil. I forgot to mention that the house is in a tropical pine forest (humid soil and temperatures above 10ºC/50ºF on winter) and it rains somewhat frequently in this season. We have a copper ground rod that electrician did not install (for some reason they chose to connect the house's ground wire to the ground connection used for the transformer), so I guess installing that rod would help with the issue. \$\endgroup\$
    – JABN
    Commented Jan 9, 2019 at 23:37